Not sure how eQuest would handle this but could you not create an
electric boiler that is essentially the electric chiller acting as a
heater (COP of 3 versus 1) to simulate that and have a single heating
piping loop. Secondary boiler would be the purchased steam. Custom
boiler curves to simulate the electric chiller as a heater/heat pump
over a range of temperatures. Just a thought.
 
Regards, 

Kevin 
_________________________________________ 

Kevin L. Wyman,  P.E. 
LEED AP 

On-site Power Product Management 
UTC Power 
195 Governor's Highway 
So. Windsor, CT 06074 
860-727-7020 (V) 
860-660-0723 (F) 
860-882-9595 (M) 
kevin.wyman at utcpower.com 

"Fuel Cells, Microturbines and Reciprocating Engines for combined
cooling, heating and power solutions" 


________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Mark
Nieman
Sent: Wednesday, October 24, 2007 10:43 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] how to simulate a four pipe system with heat pump
chiller providing cooling in summer and heating in winter


It sounds like you may not have specified a pump for your chilled water
loop. Check the loop and see if you have a pump assigned to it. You'll
need to be mindful of your pump energy to make sure you're not
overshooting what your actual system configuration will use.
 

Mark Nieman, PE, CEM 
Sr. Energy Engineer 
McKinstry Essention 
Direct: (206) 832-8152 
Cell: (206) 510-4760 
FAX: (206) 832-8552 
http://www.mckinstry.com <http://www.mckinstry.com/>  
"For The Life Of Your Building" 

 

________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of nicole
chen
Sent: Wednesday, October 24, 2007 7:37 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] how to simulate a four pipe system with heat pump
chiller providing cooling in summer and heating in winter


Dear all
 
I am trying to simulate a four pipe system with heat pump chillers
providing cooling in summer and heating in winter and purchased steam as
supplemental heating source.I planed to build two loops for the project.
One for chilled water , another for hot water. But heat pump chillers
can only be attached to chilled water loop or two pipe loop , not hot
water loop. So I built one chilled water loop for cooling and one two
pipe loop for heating . But there is always a error message " the
chilled water loop has zero flow rate". It seemed a two pipe loop can
not be build together with other type of loop ,such as chilled water
loop or hot water loop. I have no idea of it . I want to know how to
simulate such a system. Thank you in advance. 
-- 
Yours
Nicole Chen 

==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071024/9e314e05/attachment.html 


More information about the Bldg-sim mailing list