[BLDG-SIM] eQUEST error message

Kristin Field KField at archenergy.com
Wed Oct 31 13:24:24 PDT 2007


Check the PS-C or PS-D report to see which piece of equipment is
overloaded.  That will help you diagnose what is going on in your
central plant.
 

***************************************************************
Kristin M. Field, EI
Energy Analysis Group
Architectural Energy Corporation
2540 Frontier Ave., Suite 201
Boulder, CO  80301
303.444.4149
 
 


>>> "Seth P. Spangler" <sspangle at rmf.com> 10/31/2007 12:39 PM >>>

Hello,
 
I am trying to “fix” an eQUEST model a co-worker of mine started. I get
this error message for every zone that was created. Can anyone tell me
what it references or what is causing the error?
 
System: EL1 Sys7 (SZRH) (G.WNW2)         could not successfully
             allocate all energy to the 5-minute bins during
             heating because of an equipment overload.  The peak
             load used in ECONOMICS will not include the fraction
             due to the overload, but the PLANT reports will.
             Mon/Day/Hour:  6 15  1  Energy:   8.9  Unallocated: 0.135
 
Thanks in advance for your help.
 
 
Seth Spangler, LEED® AP 
Design Engineer
RMF Engineering, Inc 
Ph: (843) 971-9639 ext:108
Fax: (843) 971-9641
sspangle at rmf.com 
 
=====================================================You received this
e-mail because you are subscribed to the BLDG-SIM at GARD.COM mailing list.
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071031/7731a30a/attachment.html 


More information about the Bldg-sim mailing list