[BLDG-SIM] LEED Building Orientation

Neuhauser, Ken Ken.Neuhauser at csgrp.com
Thu Nov 29 11:30:45 PST 2007


I am not the authority, Keith, but I believe that your interpretation
(that existing buildings do not get rotated in the baseline) is
consistent with the intent of Appendix G.  In new construction, the
decisions regarding building orientation will affect performance and
that performance should be measured against the baseline (although,
there are cases, such as a building that adjoins buildings to either
side, where rotating the baseline through all four orientations does not
make sense).  If you're improving an existing building, the existing
conditions of building enclosure components, including orientation, are
an appropriate baseline.  When we apply Appendix G to existing
buildings, we have also found that "existing building envelopes"
sometimes needs to be parsed into existing building envelope components.
For example, in a mill rehab, the bearing walls may be serviceable and
appropriately modeled "as is" in the baseline, but missing windows or
windows that are clearly not serviceable we model as per the ASHRAE
minimum compliance.

 

You should note, also, that an addendum to the standard has removed the
provision in the table under G3.1, 5c to distribute windows uniformly in
horizontal bands across the four orientations.  That should make all of
our lives easier.

 

Regards,

Ken Neuhauser, M.Arch, MSc.Arch, LEED AP

Architectural Project Manager

Conservation Services Group, Inc.

40 Washington Street

Westborough, MA 01581

Ph. 508 836-9500 ext. 13226

Fax 508 836-3181

www.csgrp.com <http://www.csgrp.com/>    

 

 

 

________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Keith
Lane
Sent: Tuesday, November 27, 2007 2:40 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] LEED Building Orientation

 

I am modeling an existing building for Energy & Atmosphere Credit 1:
Optimize Energy Performance. In LEED and table G3.1 No. 5(a) of ASHREA
Standard 90.1-2004, it states that "the baseline building performance
shall be generated by simulating the building with its actual
orientation and again after rotating the entire building 90, 180, 270
degrees, then averaging the results". However table G3.1 No. 5(f) of
ASHREA Standard 90.1-2004 states: "for existing building envelopes, the
baseline building design shall reflect existing conditions prior to any
revisions that are part of the scope of work being evaluated." Would
this mean that you do not need to simulate the building for the four
orientations? It just doesn't seem to make sense to simulate the
building in such a manner if it is existing. I am new energy modeling
for LEED credit and sincerely appreciate any assistance.

 

Thank you,

 

Keith Lane, LEED AP

Mechanical Engineer

Garcia.Galuska.DeSousa

Consulting Engineers                     Inc.                        

370 Faunce Corner Road, Dartmouth, MA 02747 

p.508.998.5700                          f. 508.998.0883

 

 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071129/4bee6130/attachment.htm>


More information about the Bldg-sim mailing list