[BLDG-SIM] Baseline HVAC Type
gail
gail22 at gmail.com
Tue May 15 15:34:59 PDT 2007
Hi Bill,
I'm of the opinion that many laboratory spaces DO meet the intent of this
exception and MAY be modeled with PSZ systems. The basis for my opinion is
the 90.1-2004 User's Manual, Section 6.5.2.1, which specifically mentions
"areas of hospitals, operating rooms, and laboratories that must be
maintained @ positive or negative pressures to prevent contaminants from
entering" as examples of zones where special pressurization relationships,
cross-contamination requirements, or code-required minimum circulation rates
are such that variable air volume systems are impractical. Also, laboratory
spaces often have high process loads meeting or exceeding the 10 Btuh/sqft
threshold when compared against adjacent hallways, offices, and/or
classrooms.
If I were preparing LEED Documentation for a V2.2 lab building, I would
probably provide an accompanying narrative that specifically references the
Appendix G exception, and the User's guide Section 6.5.2.1 clarification.
Best Regards,
Gail Stranske
CTG Energetics
On 5/15/07, Bill Talbert <btalbert at aeieng.com> wrote:
>
> Can anyone provide feedback on the intent of ASHRAE 90.1 Appendix G
> Exceptions to G3.1.1 which allow changes to the baseline HVAC systems
> prescribed in Tables G3.1.1A and G3.1.1B for spaces with special
> pressurization requirements or spaces where peak thermal loads differ by
> more than 10 Btu/h-sqft? This exception would appear to allow Packaged
> Single Zone air conditioners with gas-fired heating as baseline systems in
> laboratory spaces with high equipment loads and/or pressurization
> requirements. In a large lab building where the baseline system per Table
> G3.1.1A is a VAV system, this could make a big difference in calculated
> energy savings. A recent CIR (February '07) on the USGBC site implies that
> the exception should not be used although the question involves reheat
> issues as well. It seems that a PSZ system could be modeled successfully to
> meet zone conditions without reheat but does this approach (simulating the
> baseline for a large laboratory building with multiple PSZ systems) meet the
> intent of the exception? Has anyone else had any experience with this or
> can the A90.1 and LEED folks offer some perspective?
> Thanks,
>
>
>
>
>
>
> Bill Talbert, PE, LEED(r) AP
> Mechanical Systems
> Phone: (608) 441-6677
> E-mail: btalbert at aeieng.com
>
> Affiliated Engineers Inc.
> 5802 Research Park Blvd.
> Madison, WI. 53719
> Tel. (608) 238-2616
> Fax. (608) 238-2614
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070515/7f841f6f/attachment.htm>
More information about the Bldg-sim
mailing list