Zoning will always be the same in both buildings. Each zone will be
served by either a single zone system or a central system depending on
the mapping.
Use the system mapping in Table G.3.1.1A and B. The baseline system is
determined based on residential or non-residential, size (if
non-residential) and the fuel source for the proposed design.
The mapping may be giving you a lot of (inefficient?) single zone units,
App G is designed to give you credit for using a more efficient overall
system in that case. If you meet one of the size thresholds, then you
will take your existing zones and serve them from a central VAV system
of some type, even though you have smaller distributed systems in your
proposed design.
If you haven't picked up the standard's user manual yet, that would be a
good acquisition. Otherwise I don't know of much - Google does a great
job of searching through bldg-sim history. Include "bldg-sim" in your
search, or use the search function off of Gard's page.
David
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Caleb Rockenbaugh
Sent: Thursday, March 01, 2007 12:55 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] eQuest/baseline basics/ZONING, etc.
Thanks for the previous feedback...
A general question on the (eQuest) Baseline and Proposed that I
wasn't able to clarifiy in Appendix G:
When you have a complete system for the propsed
building-multiple zones, same level, each serve by GSHP-is the baseline
to model the same zones with the baseline mechanical system in each, say
PSZ-AC? Or is it appropriate to model with a single system serving all
the zones in each case model?
In this regard, has anyone found in their pursuits of energy
modeling a resource to cover such general questions as this?
Thanks Again,
caleb
CALEB ROCKENBAUGH PE, LEED AP
P C D - E N G I N E E R I N G S E R V I C E S
184 WETTERHORN WAY LONGMONT, CO 80501
303.678.1108 T
303.678.1142 F
WWW.PCDENGINEERING.COM <http://www.pcdengineering.com/>
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.4/702 - Release Date:
2/25/2007 3:16 PM
--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.4/702 - Release Date:
2/25/2007 3:16 PM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070301/9cb0e9cd/attachment.htm>
More information about the Bldg-sim
mailing list