[BLDG-SIM] 90.1-2004 ASHRAE Basecase

Larry Degelman ldegelman at suddenlink.net
Mon Mar 5 17:21:32 PST 2007


Apply caution here, because F-values are conductance per lineal foot and
not per square foot.  They are meant to apply to slab perimeters and not
floor slab areas.  You would incur significant errors if you multiply
F-values by areas.  C-values are basically the same as U-values, but
without outside surface conductance coefficients (like air films).
 
Regards,
 
LOD
================================================
Larry O. Degelman, P.E.          <mailto:ldegelman at suddenlink.net>
ldegelman at suddenlink.net
Professor Emeritus of Architecture     1-979-696-2506
Texas A&M University
================================================
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Aulbach,
John
Sent: Monday, March 05, 2007 5:01 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 ASHRAE Basecase
 
ASHRAE 90.1-2004, page 7 - Definition of F-Factor (loss through
slab-on-grade floor), page 6 - Definition of C-Factor (loss through
underground wall). Note units are the same as U-Value. I believe you use
them for the same purpose as U-Factor, except your outside medium isn't
air, it is dirt.
 
  _____  

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Steve
Mignogna
Sent: Monday, March 05, 2007 2:37 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 ASHRAE Basecase
Hello,

I had a question regarding setting up a baseline model based on the
ASHRAE 90.1-2004 standard.  For the envelope requirements, the required
values for the "Slab on Grade Flrs" and "Below Grade Walls" are in terms
of "F-values" and "C-values" respectively.  Since eQuest only takes the
U or R values as inputs, I was wondering how these F and C values
corresponded to them.  Any help would be greatly appreciated. 

Regards,

-- 
Steve Mignogna
Atelier Ten 
 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070305/d16c4e4b/attachment.htm>


More information about the Bldg-sim mailing list