[BLDG-SIM] Process Loads and LEED

neeraj near_ej at yahoo.com
Tue Mar 6 12:13:42 PST 2007


I agree with Vaibhav.

Though, the following comment is for someone who does not make it to 25% as proposed in the design: In the past, for LEED 2.2 we have quantified the probable diversity of the receptacles to a reasonable detail. We found that no matter what the stretch of imagination the building will not exceed 13% of total energy cost. Having shown our case, we earned  the credits we sought for. "God is in the details" -- or probable details (shown in an exception calculation)!

Best regards,
Neeraj 

----- Original Message ----
From: Vaibhav Potnis <vaipotnis at hotmail.com>
To: BLDG-SIM at gard.com
Sent: Monday, March 5, 2007 4:32:59 PM
Subject: [BLDG-SIM] Process Loads and LEED

Great discussion on the LEED aspects of Process Loads.

However I wanted to point out that for a LEED energy analysis, process energy has to be maintained at 25% of total energy cost of the Baseline Building Performance ( LEED- 2.2 Ref Guide page 182). I prefer taking exceptional calculatins for process energy to simplify the calculations as well as the review.

Hope this helps.



Vaibhav Potnis 
www.greenbuildingservices.com

 






From: "Brandon Nichols" <BrandonN at Hargis.biz>
Reply-To: BrandonN at Hargis.biz
To: <BLDG-SIM at gard.com>
Subject: [BLDG-SIM] Process Loads and LEED
Date: Mon, 5 Mar 2007 11:05:04 -0800




 

Varkie,


 

Something we have been noticing in schools lately is a high receptacle load, which we believe is attributable to increased usage of computers, approaching and in some areas exceeding 5 W per square foot -- the kinds of loads I used to figure for "technology intensive" office areas just a few years ago.

 

In researching an energy question for a school today, I came across this web page and case study which I thought was relevant to your question:

 

http://www.energystar.gov/index.cfm?c=power_mgt.pr_power_management

 

http://www.energystar.gov/ia/products/power_mgt/North_Thurston_Case_Study.pdf

 

Essentially they summarize how, by consistently implementing power management on computer monitors and CPUs using a simple utility program, a cost savings of an estimated $15-$30 per computer per year can be realized (on personal workstations I would add, not systems required to be continuously online).  Multiplied across thousands of computers, the bottom line annual savings can be substantial.

 

How to account for this in energy modeling software I have a general idea:

 

1) Assign the baseline receptacle load to "occupied hours"; e.g. 5 W/SF 'always on'

2) Assign a diversified receptacle load schedule to the alternate analyses

 

But quantifying the diversified load schedule is the hard part -- it will no doubt vary significantly depending on the occupancy.  Though not fully developed, this may provide a starting point for one method to reduce process electrical loads in a LEED analysis.

 

 

Regards


 
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart St
Suite 1000
Seattle, WA 98101
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
www.hargis.biz




From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Varkie Thomas
Sent: Monday, March 05, 2007 7:14 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Process Loads and LEED





LEED-NC Version 2.2 page 173 "Optimize Energy Performance" states "Demonstrate a percentage improvement in the proposed building performance -- " and  "For the purpose of this analysis, process energy is considered to include, but is not limited to, office and general miscellaneous equipment, computers, elevators & escalators, kitchen cooking & refrigeration, laundry washing & drying --- "

On page 174 "For EA Credit 1, process loads shall be identical for both the baseline building performance and the proposed building performance"

Assuming the same space process load is used in the baseline and proposed, then a building with a receptacle load density of say 1.0 w/sf will produce a much greater percent savings compared to the same building with a receptacle load density of say 6 w/sf.

Page 173 "must comply with the mandatory provisions (Sections --- ) in Standard 90.1-2004 (without amendments)"  There is no mention of Standards 62 for ventilation & occupancy density or Standard 55 for indoor comfort conditions.  Does this mean that the baseline can be based on the proposed ventilation, occupancy density and indoor comfort conditions?  According to Standard 62-2004 the occupancy density for general office space is 200 sf/P (from 142 sf/P in 62-2001 and I think 100 sf/P earlier).  This produces a low percent system outdoor air and energy conservation measures such as "occupancy based ventilation" and "outdoor air to relief air heat recovery" have little effect.  Std 62-2004 (also Std 90.1-2004 for lighting) provides design criteria for a limited number of space types such as a prison cell (improved from 50 sf/P & 20 cfm/P in 
62-2001 to 40 sf/P & 10 cfm/P in 62-2004) .  This makes it difficult to determine baselin e conditions using Std 62.

I am looking at a financial institution building with high occupancy and receptacle load densities.
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
=====================================================You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM



Crave for a healthier lifestyle? Ask an expert 
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM








 
____________________________________________________________________________________
Now that's room service!  Choose from over 150,000 hotels
in 45,000 destinations on Yahoo! Travel to find your fit.
http://farechase.yahoo.com/promo-generic-14795097

===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070306/3b78eac6/attachment.htm>


More information about the Bldg-sim mailing list