[BLDG-SIM] Mechanical ventilation system

Peter Alspach peter.alspach at arup.com
Thu Mar 8 17:44:09 PST 2007


My interpretation is that this is not a naturally ventilated space. You
would need to provide filtered air in the quantities stipulated by the
Standard. I would assume that MERV 13 filtration is required by LEED.
The presence or absence of certain coils does not change the fact that
this system distributes fresh air through mechanical means to each
space.

________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Virdi
Permana
Sent: Tuesday, March 06, 2007 8:53 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Mechanical ventilation system



Hello All,

I hope these questions are allowed to be addressed in this group:

 

If a building does not have heating and cooling system but has
mechanically ventilation system, is it still considered a natural
ventilated building as the section 5.1 of Standard 62 suggests?

Does this building need to follow section 6 of the standard 62?

How about its compliance with EQ c5, does it need to have MERV 13 air
filters?

 

Any information is greatly appreciated.

Thanks

 

Virdiansyah "Virdi" Permana

EMSI

Energy Analyst

(202) 291 3102 T

(202) 291 3107 F 

 


==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070308/6d1853a8/attachment.htm>


More information about the Bldg-sim mailing list