[BLDG-SIM] Equest 3-61

Fred Porter fporter at archenergy.com
Thu Jun 21 13:35:17 PDT 2007


The DOE-2.2 engine has the capability to specifically model an ice rink!
The keywords just never made it into the eQUEST interface. You need to
manually edit your input file. Search the DOE-2.2 "Dictionary" pdf for
"ice" and/or "ice-rink." Most or all of the unique keywords are in the
ZONE command. The brine chiller will probably need to be defined by
custom curves as it supplies 20F fluid. 

 

Then run the dll or exe bdl/sim versions of DOE-2.2 instead of eQuest.

 

Having said that, many of the most efficient AHUs now used to condition
these spaces are not well-represented by the systems modeled directly in
DOE2.2/eQUEST.

 

--

Fred 

 

  _____  

From: Audra Dybdahl [mailto:adybdahl at WoodHarbinger.com] 
Sent: Thursday, June 21, 2007 12:25 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Equest 3-61

 

I am currently modeling a hockey arena.  There will be a chilled water
system installed for year round ice maintenance.  Has anyone had any
experience with modeling this type of application?  Is it possible to
have a chilled radiant slab?

 

Thanks for your help,

 

Audra Dybdahl

Wood Harbinger, Inc.

3009 112th Ave. N.E., Ste. 100

Bellevue, WA 98004

425-822-9499

 

 
 
>'>
 New RomanYou received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM




===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070621/59c1fac4/attachment-0002.htm>


More information about the Bldg-sim mailing list