[BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case

gail gail22 at gmail.com
Thu Jul 12 12:38:32 PDT 2007


The way it is written (and the way we've been instructed to review it as
USGBC LEED reviewers), you are permitted to apply any of the addenda to your
project.  However, for each addendum you choose to apply, the entire
addendum applies, and it applies to any other relevant LEED points.  Paul's
example is correct: since both the 25,000 square foot threshold and the
normalized glazing revision are included as part of addendum a, you would
have to follow both of these requirements if you choose to apply that
addendum to the project.  However, you are not required to apply other
addenda to the project just because you chose to follow addendum a.

Best Regards,
Gail Stranske
CTG Energetics, Inc.

On 7/12/07, Michael Tillou <michael.tillou at gmail.com> wrote:
>
> Paul,
>
> My interpretation of the USGBC ruling is the same as yours, I think.  You
> cannot pick and choose which items in ASHRAE addenda to use on your LEED
> project.  You have to choose either 90.1-2004 with no addenda or 90.1-2004
> with addenda which would include ALL the published adddenda that apply to
> ALL chapters of 90.1-2004 not just Appendix G.  There are currently 42
> addenda to ASHRAE 90.1-2004 (a-v,x,y,aa-ae,ag-ar,av...I hope I didn't miss
> any) This decision would also impact your compliance with the EA energy
> performance pre-requisite.
>
> As you said "messy".
>
> I think that all the 90.1-2004 addenda will eventually be published as
> ASHRAE 90.1-2007 which will simplify keeping track of all the changes.
>
> Regards,
>
> Mike
>
> Michael Tillou, PE, LEED
> Tillou Engineering, LLC
> Williamstown, MA 01267
> P: 413-458-9870 C: 413-652-1087
>
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Paul
> Riemer
> Sent: Wednesday, July 11, 2007 4:22 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
>
>
> Has anyone read the fine print referenced in these strings to reach this
> conclusion:
>
> If you are modeling under 90.1-2004 Appendix G for LEED and opt to not
> normalize the glazing by orientation under addendum a, then you must also
> except the other portions of addendum a, most notably the revised area
> threshold of 25,000 sf for the base HVAC system in Table G3.1.1A.
>
> It seems like a messy and perhaps unintentional convergence of standard
> and
> policy adoption but it also seems like it is there in black and
> white.  Any
> other conclusions?
>
> Thanks,
> Paul Riemer
> The Weidt Group
>
>
>
>
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Michael
> Rosenberg
> Sent: Wednesday, May 16, 2007 12:47 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
>
> The requirement to  distribute fenestration uniformly in horizontal bands
> across the four orientations has been removed from Appendix G in the
> published Addenda Supplement to 90.1, 2004. See the ASHRAE website for the
> supplement.
>
> http://www.ashrae.org/technology/page/132
>
>
>
>
> Michael Rosenberg
> Oregon Department of Energy
> 625 Marion St. N.E.
> Salem, OR 97301-3742
> Phone : (503) 373-7809
> Fax: (503) 373-7806
>
> >>> Chris Jones <cj at cr-jay.ca> 5/16/2007 9:56:02 AM >>>
> Appendix G notes that for the Baseline building: "Vertical fenestration
> areas for new buildings and additions shall equal that in the proposed
> design or 40% of gross above grade wall area, whichever is smaller, and
> shall be distributed uniformly in horizontal bands across the four
> orientations."
> Does this mean that the Baseline building gets windows on all walls on
> each
> orientation whether or not the Design case has a window in all walls on
> each
> orientation.  For example, if the west orientation has 30% glazing overall
> but many spaces have no windows - some walls on the west face have more
> that
> 30%.  Do those spaces in the Baseline case get 30% glazing?  Or do I only
> put windows in the Baseline case where there are windows in the Design
> case.
>
> Thanks for any help!
>
>
>
>
>
>
>
> Chris Jones, P.Eng.
> 14 Oneida Avenue
> Toronto, ON M5J2E3
> Tel. 416 203-7465
> Fax. 416 946-1005
>
> ======================================================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM
> mailing list.  To unsubscribe from this mailing list send a blank message
> to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
> ======================================================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM
> mailing list.  To unsubscribe from this mailing list send a blank message
> to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
>
> ------------------------------------------------------------------------
> --------
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Leonard
> Sciarra
> Sent: Tuesday, May 15, 2007 8:52 AM
> To: BLDG-SIM at gard.com
> Cc: Scott Foster
> Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
> Decision impacting EAc1 Credit )
>
>
> FYI,
> these are current addenda
> Standard 90.1-2004, Energy Standard for Buildings Except Low-Rise
> Residential Buildings (I-P and SI versions) The first Addenda Package
> includes a, b, c, d, e, f, g, h, i, j, k, l, m, n, o, p, r, s, t, u, v, x,
> and ak Addendum ad is listed separately in the second Addenda package.
>
> Standard 90.1-2004: Addenda Supplement Package (PDF) Standard 90.1-2004:
> Addendum ad (PDF) link
>
> http://www.ashrae.org/technology/page/132
>
> Leonard Sciarra, AIA, LEED ap
>
> 312.577.6580 (Dir)
>
> G E N S L E R | Architecture & Design Worldwide
>
> 30 West Monroe Street
>
> Chicago IL, 60603
>
> 312.456.0123
>
> leonard_sciarra at gensler.com
>
>
>
>
>
> ------------------------------------------------------------------------
> --------
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Brandon
> Nichols
> Sent: Monday, May 14, 2007 6:11 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
> Decision impacting EAc1 Credit )
>
>
> Thanks Gail very much for the notification,
>
> And thanks to whomever was responsible for convincing USGBC to amend the
> process.  Seems like just a month ago I was railing on about this very
> topic; now I'm out of excuses for not drafting up an ASHRAE 90.1 Appendix
> G
> amendment to address shortcomings in the baseline building rotation
> exercise.
>
>
> Regards,
>
> Brandon Nichols, PE
> Mechanical
> HARGIS ENGINEERS
> 600 Stewart St
> Suite 1000
> Seattle, WA 98101
> d | 206.436.0400 c | 206.228.8707
> o | 206.448.3376 f | 206.448.4450
> www.hargis.biz
>
>
>
> ------------------------------------------------------------------------
> --------
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of gail
> Sent: Monday, May 14, 2007 3:02 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] ASHRAE Addendum now allowed for LEED (Major LEED
> Decision impacting EAc1 Credit )
>
>
> Dear Fellow Energy modelers,
>
> The following posting has been placed on the USGBC website (
> http://www.usgbc.org/ShowFile.aspx?DocumentID=2664), which allows the use
> of
> ASHRAE Addenda for all credits referencing ASHRAE standards.
>
>
> Use of approved Addenda for ASHRAE Standards referenced in LEED
>
> Background:
> ASHRAE currently publishes Continuous Maintenance standards every three
> years, with a Supplement published eighteen months after the Standard is
> published. In rare cases, addenda are published in between the
> eighteen-month periods. LEED development and ASHRAE standards development
> are not aligned and many addenda have been approved that would be useful
> for
> LEED project teams.
>
> Action:
> LEED project teams are required to use the ASHRAE Standard referenced in
> the
> applicable Reference Guide and are permitted to use addenda within the
> most
> recent Supplement to that Standard, as well as any approved addenda
> published in between the eighteen-month periods. Project teams are
> responsible for notifying LEED reviewers of the use of ASHRAE addenda
> utilized at the time of project documentation submission.
> If a project team elects to use an addendum to an ASHRAE Standard, this
> addendum must be applied to the entire LEED submittal.
> This should make fenestration modeling much easier for the Baseline Case
> for
> projects opting to follow the Addendum.
>
>
>
>
> Best Regards,
>
> Gail Stranske
>
> CTG Energetics, Inc.
>
>
>
>
>
> ==================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM
> mailing list.  To unsubscribe from this mailing list send a blank message
> to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> ==================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM
> mailing list.  To unsubscribe from this mailing list send a blank message
> to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
>
>
> ==================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM
> mailing list.  To unsubscribe from this mailing list send a blank message
> to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070712/713559f2/attachment-0001.htm 


More information about the Bldg-sim mailing list