[BLDG-SIM] ASHRAE 90.1-2004 App. G, Hospital Baseline
Dana Troy
DTroy at glumac.com
Mon Jul 23 10:25:24 PDT 2007
Hello all,
I am currently working on the ASHRAE 90.1-2004, Appendix G baseline model of a hospital in Oregon. The part of the building being analyzed is a 40,000 sf, 3 story addition to an already existing building of approximately 90,000 sf. I am having some issues determining what to use for the baseline HVAC system. Here are some key details of the current as-designed building:
* Reheat fan system
* Constant volume, 60,000 cfm
* 100% outside air
* Draws heat from two boilers and two chiller in a central utility plant that also serves the rest of the building
These design parameters lead to some confusion when selecting the HVAC baseline systems. For example:
* Since the addition is served by a system that serves the entire building, should building be modeled as an ~130,000 sf building? This would make it System 5 under Table G3.1.1A. Problems with this are that it calls it out to be a PVAV w/ reheat, which is not a legitimate comparison. If the baseline is supposed to be PVAV, the OSA requirements need to be the same anyways (G3.1.2.5), therefore effectively making it a constant volume system.
* Should the sf be taken relative to only the addition (40,000 sf)? This is also not a fair comparison between the two systems because the addition draws heating and cooling from a system designed for a much larger square footage.
I guess my main questions are if anyone has dealt with large, constant volume, 100% OSA systems and their baseline HVAC systems and if anyone has modeled additions that are served by a larger CUP.
Thanks for any help in advance.
Dana Troy, EIT
Energy Analyst
<http://www.glumac.com/>
_____
320 SW Washington, Suite 200
Portland, OR 97204-2640
T. 503.227.5280 F. 503.274.7674
D. 503.345.6286
Thinking. Inside the building.
www.glumac.com <http://www.glumac.com/>
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070723/21563df0/attachment-0001.htm
More information about the Bldg-sim
mailing list