[BLDG-SIM] Exterior Lighting

Brandon Nichols BrandonN at Hargis.biz
Fri Jul 6 08:35:41 PDT 2007


Hello Tara,
 
See screen 23 of the eQuest DD wizard.  There is an input for exterior
lighting in watts per square foot for the selected shell.  This
unfortunately is not the way exterior power is more generally
characterized, namely as watts per linear foot of perimeter.  
 
The input number is stored in the pd2 file, and is multiplied by the
shell square footage to obtain the EXTERIOR-POWER value in kilowatts
found in the inp file.  The EXT-USAGE keyword looks like it's used only
to assign exterior power to a particular electric meter.
 
Generally I assign all the exterior lighting load to the first floor
Shell.  You might try entering the data as described above into the
wizard, then saving the file and searching for the keywords you're
looking for in the inp file to see the syntax of how they're used.
 
HTH...
 
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS

600 Stewart Street

Suite 1000

Seattle, WA 98101

www.hargis.biz

 

d | 206.436.0400  c | 206.228.8707

o | 206.448.3376  f  | 206.448.4450

 
 

  _____  

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Tara
Streck
Sent: Thursday, July 05, 2007 4:57 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Exterior Lighting


I am working on adding exterior lighting loads to a building simulation
and understand that eQuest responds to EXTERIOR-POWER and EXT-USAGE as
commands for this input. However, I am unsure when to enter this
information in the .inp file or what the code might look like. Has
anyone had experience with exterior lighting?
 
Thank you,
 
Tara Streck
Mechanical Engineer
LEED Accredited Professional
Wood Harbinger, Inc.
Mechanical/Electrical Engineers
3009 112th Ave NE, Ste 100
Bellevue, WA 98004-8008
(425) 822-9499
(425) 822-4338 Fax
tstreck at woodharbinger.com <blocked::mailto:tstreck at woodharbinger.com> 
www.woodharbinger.com
 

==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070706/52127090/attachment.htm>


More information about the Bldg-sim mailing list