[BLDG-SIM] central heat pumps and circulation loops

Michael Haughey mhaughey at earthlink.net
Thu Jul 12 16:13:35 PDT 2007


Hi Aleka,
 
A different sort of question comes to mind.  Once heated to 180F, what is
the fluid return temperature?  If above 110F it seems like it will heat the
geothermal loop from the boiler.  Another possibility is to select the
fan-coils units to work using the 110F supply.  Otherwise, the
fan-coil/boiler loop may need to be completely separate.
 
Good luck,
 
Michael Haughey
 
Silvertip Integrated Engineering Consultants
303-650-1080
Cell:  303-903-4722
Fax:  303-430-1402
mhaughey at earthlink.net
 

  _____  

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Aleka Pappas
Sent: Thursday, July 12, 2007 10:55 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] central heat pumps and circulation loops


Hi all,
I'm trying to model a central ground water source heat pump serving hot &
cold water loops for a radiant heating & cooling system in eQuest.  The 110
F hot water loop from the heat pump (loop to loop HP type chiller) serves
the radiant system directly, and has a secondary loop with a boiler attached
to it to bring the temperature up from 110 F to 180 F to serve some fan coil
units.  
I'm having a hard time configuring the loops and plant equipment to even
approximate this system.  Has anyone tried to model something like this in
eQuest?  From what I understanding, you can't put a boiler on a secondary
loop, and I'm hitting a wall with that.  If I put the boiler and the HP on
the same primary loop, I get errors that tell me 180 F is too high a
temperature for a GSHP water loop.  The closest I seem to be able to get is
to model the system with two separate HW loops - one for the fan coils with
only a boiler and one for the radiant system with the HP.  But, then I can't
use the heat pump to preheat for the FCU loop with this model.  

Any thoughts?

Thanks,
Aleka



======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070712/688a6d40/attachment.htm>


More information about the Bldg-sim mailing list