[bldg-sim] Min Outdoor Air

Aulbach, John jaulbach at nexant.com
Tue Jan 30 14:15:08 PST 2007


Steve:
 
What type of HVAC system are you running? A VAV system Outside air will only see the mixing with return air upstream of the coil. The cooling coil will adjust as required to maintain the 55 °F setpoint need as outside conditions change.  Downstream, the reheat coils will never see the outside conditions.
 
Correct me if I am wrong...

________________________________

From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Steve Barnell
Sent: Tuesday, January 30, 2007 1:54 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] Min Outdoor Air


Hello,
 
I am modelling a building in Canada with eQUEST and have several runs varying the min OA rate. In comparing the runs I noticed that the cooling comsumption varied as expected however the Space Heating comsumption is not altered. This seems counter intuitive to me. Any ideas?
 
-Steve

--  <http://a8-asy.a8ww.net/a8-ads/adftrclick?redirectid=en-mail_a_01>  


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070130/a8e6e306/attachment.htm 


More information about the Bldg-sim mailing list