[bldg-sim] steam meters in eQuest
Mark Nieman
MARKN at McKinstry.com
Fri Feb 2 13:09:09 PST 2007
Here's one way that will work using steam meters. Set up equipment in
the Wizard using a typical water cooled chiller and natural gas boilers.
Then switch to "Detailed Data Edit" under the "Mode" menu.
1. Go to the Water-Side HVAC button that shows the water loop diagrams.
In the left panel Component Tree, right-click on the project title at
the top and select "Create Steam Meter..." Name your meter and create
from scratch. Attach it to your DHW loop. Edit as needed. Next, select
the DHW boiler and right click it in the Component Tree, select "Delete"
and erase the boiler from the DHW loop. Do the same process for your
building hot water loop.
2. Create an absorption chiller hot water loop by right-clicking on the
project name at the top of the Component Tree. Name the loop, create
from scratch and set loop type to hot water. Set your HW temp to 230F or
whatever is appropriate for your steam pressure going to the chiller
(steam is not explicitly modeled in eQUEST). Assign a new steam meter to
that loop like in item 1 above.
3. Create a new steam meter for the building hot water loop.
4. Double-click on your chiller and change it to an absorption chiller
(1 or 2 stage) and assign it to your chilled water, condenser and
absorption hw loops.
5. Next, click the Utility & Economics button and create a new Utility
Rate. Name it, create from scratch and set the type to Steam. Assign
your three new steam meters to the rate under "Steam Meters Served" in
the General tab. Assign a Uniform Energy Charge if appropriate under the
Energy/Demand tab. You'll have to calc what the effective $/unit is
based on the condensate billing. Remember this is calculated based on
steam, not condensate, so you'll have to factor in losses.
The PS-B report is a good summary of each electric and steam meter.
Total steam use will be summarized in the PS-E report for all steam
meters added together and PS-F shows each meter separately.
Mark Nieman, PE, CEM
Sr. Energy Engineer
McKinstry Essention
Direct: (206) 832-8152
Cell: (206) 510-4760
FAX: (206) 832-8552
http://www.mckinstry.com <http://www.mckinstry.com/>
"For The Life Of Your Building"
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Vicki
Lynne
Sent: Thursday, February 01, 2007 11:58 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] steam meters in eQuest
Hello - I'm relatively new to eQuest (though have used other modeling
software extensively) and I'm modeling a building on a campus with a
central steam plant. The building is billed for steam use based on
gallons of condensate returned. The building has steam-hot water heat
exchangers for the MZ air handling units and the DHW system. It also
has an absorption chiller on the steam loop. There is no natural gas
use in the building. I set up steam meters in the loops for these "end
uses" but I'm running into problems. I searched the archives and found
a couple questions posted in past years about steam meters but didn't
really find the answers I need.
1) I can't directly model the DHW w/steam so apparently I have to model
it as natural gas? Or can I model it as a direct load in the steam
meter properties - direct load screen?
2) No steam use is showing up when I run the simulation. I went into
the Master Meter screen and it only allows (apparently) electric and
fuel meters. Under fuel meters, there is not a steam option, unless one
is supposed to select "other". Does the Master meter need to know about
the steam meters? And if so, how do I tell it? Is there something else
entirely that I should be doing that I'm missing? (Since eQuest's help
screen is a DOE2 help screen, I'm not having much luck with
understanding how it applies to eQuest in this case.)
Vicki Lynne, PE
National Center for Appropriate Technology
Butte, MT
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
This email is the property of McKinstry or one of its affiliates and may contain confidential and/or privileged information. If you are not the intended recipient or have received this e-mail in error please notify the sender immediately and delete this e-mail.
Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden.
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070202/494de1a0/attachment.htm>
More information about the Bldg-sim
mailing list