[bldg-sim] eQUEST window baseline
Vikram Sami
VSami at lasarchitect.com
Thu Feb 15 10:27:26 PST 2007
Andrew,
You can adjust proportions of windows globally using the global
parameter functions in eQUEST. You have to write an expression for the
window height and width with respect to their parent entity (wall in
this case) that will look something like this
for height : #P("HEIGHT")*#PA("insert global parameter name here")
Note: the values within the quotes are case sensitive
You can now control the height globally by changing the global parameter
value.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Andy
McNamara
Sent: Thursday, February 15, 2007 12:39 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST window baseline
Hello,
I am creating an energy model for a LEED project. In "baselining" the
building, one of the stipulations of ASHRAE 90.1 2004 is that the
windows must be evenly distributed in horizontal bands on each facet of
the facade. My building has 17 facets due to a somewhat complicated
design and I am wondering if anyone knows a relatively straightforward
way to accomplish that distribution. One of my problems is that in the
Design Development Wizard, there are only 4 areas in which to enter
percentages (N., E., S., W.) which doesn't seem to work on a building
with so many facets. On the other hand, it seems tedious to go into
each window and adjust its percentage. Is there a more elegant way to
adjust window proportions globally? I am thinking a parametric run
might be the best solution. Can anyone provide some insight on this?
Thank you!
Andrew McNamara
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070215/e57f9c45/attachment.htm>
More information about the Bldg-sim
mailing list