[BLDG-SIM] Fwd: eQUEST HVAC sizing runs

gail gail22 at gmail.com
Thu Feb 15 15:27:22 PST 2007


Andrew makes a good point.  Set either system or plant sizing factors to
1.15 & 1.25 respectively, but not both.

Gail Stranske


On 2/15/07, Andrew Craig <andrew_c at ieice.com> wrote:
>
>  Assuming you are using eQUEST, in the Detailed Edit mode, you can specify
> the ratio of equipment sizing that you want for both heating and cooling.
> So to specify the Appendix G baseline model, you would oversize cooling by a
> factor of 1.15 and heating by a factor of 1.25.  Take care to check what
> the system sizing ratio is set at as well so you don't add safety factor
> upon safety factor.  Good luck.
>
>
>
>
>  ------------------------------
>
> *From:* bldg-sim at gard.com [mailto: bldg-sim at gard.com] *On Behalf Of *Andy
> McNamara
> *Sent:* Thursday, February 15, 2007 12:48 PM
> *To:* bldg-sim at gard.com
> *Subject:* [bldg-sim] eQUEST HVAC sizing runs
>
>
>
> Hello,
>
> As I mentioned previously, I am creating an energy model for a LEED
> project.  In "baselining" the building, one of the stipulations of ASHRAE
> 90.1 2004 is:
> "G3.1.2.2 Equipment Capacities.  The equipment capacities for the baseline
> building design shall be based on sizing runs for each orientation and shall
> be oversized by 15% for cooling and 25% for heating"
>
> I think that means I use "auto-size", but then how do I capture what that
> size is and oversize it accordingly?  I am guessing that the results may be
> in the SIM file.  Can anyone provide tips for executing this?  Is there a
> better way to do that auto-sizing for each orientation?
>
> Thanks,
> Andrew McNamara
>
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
>
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070215/795efcf0/attachment.htm 


More information about the Bldg-sim mailing list