[BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest

Brandon Nichols BrandonN at Hargis.biz
Thu Aug 30 14:27:34 PDT 2007


Lan, see this post...
 
http://elcca-exchange.blogspot.com/2007/04/equest-parametric-sensible-heat.html
 
Here's an excerpt:
 
$ FLOAT gives maximum heat recovery but recovers even unwanted heat, so
$ use this setting for temperature control
ERV-TEMP-CTRL = MIXED-AIR-RESET
 
Also, the ΔT between exhaust and OSA is typically not great, even if its 110°F outside and your exhaust/relief is 85°F, the ΔT is only 25°F -- compare that to even a mild winter condition of 35°F, where the ΔT is double at equivalent exhaust temperature (i.e 85 - 35 = 50°F).
 
Regards
 
Brandon Nichols, PE, LEED(r) AP
Mechanical
HARGIS ENGINEERS

600 Stewart Street

Suite 1000

Seattle, WA 98101

www.hargis.biz

 

d | 206.436.0400  c | 206.228.8707

o | 206.448.3376  f  | 206.448.4450

 
 

  _____  

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Lan Hu
Sent: Thursday, August 30, 2007 1:54 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest


Hi, all,
 
I have problem simulating ERV in eQUSET. In the program I specified ERV effectiveness around 72%, the results show 64% energy saving in heating but just 5% saving in cooling, even when I cut off all the fan tempetrature increase. Anyone has experience or suggestion?. Thank you very much.
 
Lan

  _____  

Got a little couch potato? 
Check out fun summer activities for kids. <http://us.rd.yahoo.com/evt=48248/*http://search.yahoo.com/search?fr=oni_on_mail&p=summer+activities+for+kids&cs=bz> 


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070830/af240900/attachment.htm 


More information about the Bldg-sim mailing list