[BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
J.L. Niu
Bejlniu at polyu.edu.hk
Thu Aug 30 20:00:54 PDT 2007
Therefore for summer season heat recovery, if the climate is hot and humid, total heat recovery with both moisture and sensible heat recovery can offer a better energy saving.
What is more complicated for simulation anaylsis, that total heat exchange effectiveness varies with air conditions on both sides, but a simplfied average effective can be used with reasonable accuracy.
JL Niu
----- Original Message -----
From: Brandon Nichols
To: BLDG-SIM at gard.com
Sent: Friday, August 31, 2007 5:27 AM
Subject: [BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
Lan, see this post...
http://elcca-exchange.blogspot.com/2007/04/equest-parametric-sensible-heat.html
Here's an excerpt:
$ FLOAT gives maximum heat recovery but recovers even unwanted heat, so
$ use this setting for temperature control
ERV-TEMP-CTRL = MIXED-AIR-RESET
Also, the ΔT between exhaust and OSA is typically not great, even if its 110°F outside and your exhaust/relief is 85°F, the ΔT is only 25°F -- compare that to even a mild winter condition of 35°F, where the ΔT is double at equivalent exhaust temperature (i.e 85 - 35 = 50°F).
Regards
Brandon Nichols, PE, LEEDR AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
------------------------------------------------------------------------------
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Lan Hu
Sent: Thursday, August 30, 2007 1:54 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
Hi, all,
I have problem simulating ERV in eQUSET. In the program I specified ERV effectiveness around 72%, the results show 64% energy saving in heating but just 5% saving in cooling, even when I cut off all the fan tempetrature increase. Anyone has experience or suggestion?. Thank you very much.
Lan
------------------------------------------------------------------------------
Got a little couch potato?
Check out fun summer activities for kids.
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070831/4d14cf53/attachment.html
More information about the Bldg-sim
mailing list