[BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
Brandon Nichols
BrandonN at Hargis.biz
Fri Aug 31 10:52:28 PDT 2007
Lan,
As JL suggests, if yours is a hot and humid climate, you may have better results using a heat wheel (enthalpy wheel) with total enthalpy recovery. Sensible-only as shown in my example is economical in relatively low humidity, cool-summer climates that don't provide much summertime heat recovery opportunity.
So for your project, calculate the theoretical summertime opportunity value before attempting troubleshooting with eQuest:
*
What are the estimated flow rates of the outdoor and exhaust airstreams?
*
What are the outdoor air expected summer average conditions in terms of temperature and humidity (i.e. enthalpy)?
*
What is the expected temperature and humidity of the exhaust airstream?
*
The exhaust airstream in general occupancy applications can be estimated at about 85¡ãF and 35% relative humidity, corresponding to the absolute moisture content at 55¡ãF saturation temperature from a typical cooling coil, plus 2% for people and processes.
*
Now the opportunity value of summertime heat recovery may be estimated:
*
Calculate the enthalpy difference between the outdoor summer average and the estimated exhaust airstream, and multiply by the ratio of the exhaust/OSA flow rates.
Without significant differential enthalpy between outdoor ambient average and the exhaust airstream, there simply may not be much summertime heat recovery opportunity.
Hope that helps...
Brandon Nichols, PE, LEED(r) AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
_____
From: Lan Hu [mailto:hulan199 at yahoo.com]
Sent: Friday, August 31, 2007 8:54 AM
To: Brandon Nichols
Subject: Re: [BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
Thank you very much, Brandon. After I tried used DT/DH control with rang from 5-30, I still didn't get any saving on the cooling side - the ERV sim report still show heating energy used during summer. Any more suggestion?
Brandon Nichols <BrandonN at Hargis.biz> wrote:
Lan, see this post...
http://elcca-exchange.blogspot.com/2007/04/equest-parametric-sensible-heat.html
Here's an excerpt:
$ FLOAT gives maximum heat recovery but recovers even unwanted heat, so
$ use this setting for temperature control
ERV-TEMP-CTRL = MIXED-AIR-RESET
Also, the ÄT between exhaust and OSA is typically not great, even if its 110°F outside and your exhaust/relief is 85°F, the ÄT is only 25°F -- compare that to even a mild winter condition of 35°F, where the ÄT is double at equivalent exhaust temperature (i.e 85 - 35 = 50°F).
Regards
Brandon Nichols, PE, LEED(r) AP
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
_____
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Lan Hu
Sent: Thursday, August 30, 2007 1:54 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ERV (Energy recovery ventilation) simulation in eQuest
Hi, all,
I have problem simulating ERV in eQUSET. In the program I specified ERV effectiveness around 72%, the results show 64% energy saving in heating but just 5% saving in cooling, even when I cut off all the fan tempetrature increase. Anyone has experience or suggestion?. Thank you very much.
Lan
_____
Got a little couch potato?
Check out fun summer activities for kids. <http://us.rd.yahoo.com/evt=48248/*http://search.yahoo.com/search?fr=oni_on_mail&p=summer+activities+for+kids&cs=bz>
=====================================================You received this e-mail because you are subscribed to the BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
_____
Take the Internet to Go: Yahoo!Go puts the Internet in your pocket: <http://us.rd.yahoo.com/evt=48253/*http://mobile.yahoo.com/go?refer=1GNXIC> mail, news, photos & more. .
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070831/593e920b/attachment.htm
More information about the Bldg-sim
mailing list