[BLDG-SIM] DOE2.1e HP HEAT-EIR-FPLR Problems

Xiaobing Liu XLiu at climatemaster.com
Wed Apr 4 09:23:06 PDT 2007


Chris:
 
In your message and data, It seems there are some misunderstandings about the EIR-FPLR used in the DOE-2 program. For heat pump application, which adjusts heating/cooling output by turning on and off the compressor, the value of EIR-FPLR is the actual heat pump run time during a hour. The definition of PLR is the ratio of heating/cooling demand to the heating/cooling capacity of the heat pump during a particular hour. In other word, PLR is the ideal heat pump run time without considering any cycling loss. Therefore, when PLR drops, the value of EIR-FPLR will also drop. Due to the cycling loss, the value of EIR-FPLR is usually larger than the PLR, which means the heat pump has to run a little longer to offset the cycling loss when providing required heating/cooling. The cycling loss of the heat pump can be determined from its Cycling Degradation factor (Cd), which is usually available from heat pump manufacturers.
 
BTW, If the fan power has been accounted for in the COP and the indoor fan of the heat pump will run continuously, you'd better subtract the effect of fan power when you converting COP to EIR. Otherwise, you may overestimate the fan energy consumption if you also specify a non-zero fan power in the simulation since you count the fan power twice by doing so.
 
Hope it helps,
 
Xiaobing

-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com]On Behalf Of Chris Jones
Sent: Wednesday, April 04, 2007 9:42 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] DOE2.1e HP HEAT-EIR-FPLR Problems


I am comparing the default DOE2.1e HP heating curves to the

performance data from various manufacturers.  In particular the

EIR-FPLR curve does not fit what the manufacturers show in their

data.  The default curve shows the EIR dropping as the part load

ratio drops.  My assumption is that PLR = Operating Capacity/Design

Capacity.  With the Trane, McQuay, and Waterfurnace data, the EIR

increases as the PLR goes down.  I am assuming that part load is a

result of lower flow through the unit or from higher entering dry bulb

temperature.  So when I do create my set of heating curves

HEAT-EIR-FT, HEAT-CAP-FT and HEAT-EIR-FPLR, the performance is

significantly worse than with the default DOE2.1e curves.  



Am I misinterpreting how to plot the data points for the HEAT-EIR-FPLR

curve?  Example from Trane:

COP     CAP

     

        EIR

     Ent

DB  Ent

WT  PLR

     EIR/EIR

Design  GPM

     FPLR

4.2     112000

  0.238   68

      

        68

      

        1.000

   1.000   

        

        24.5

    (1.000, 1.000)

3.1     62675

   

        0.323

   70

      20

      0.560

   

        1.355

   

        

        

        12.1

    (0.560, 1.355)

3.1     64639

   

        0.323

   70

      20

      0.577

   

        1.355

   

        

        

        18.4

    (0.577, 1.355)

3.2     65641

   

        0.313

   70

      20

      0.586

   

        1.313

   

        

        

        24.4

    (0.586, 1.313)

3.3     71123

   

        0.303

   70

      30

      0.635

   

        1.273

   

        

        

        12.1

    (0.635, 1.273)

3.4     73541

   

        0.294

   70

      30

      0.657

   

        1.235

   

        

        

        18.4

    (0.657, 1.235)

3.4     74631

   

        0.294

   70

      30

      0.666

   

        1.235

   

        

        

        24.4

    (0.666, 1.235)

3.5     79943

   

        0.286

   70

      40

      0.714

   

        1.200

   

        

        

        12.1

    (0.714, 1.200)

3.6     82643

   

        0.278

   70

      40

      0.738

   

        1.167

   

        

        

        18.4

    (0.738, 1.167)

3.6     83991

   

        0.278

   70

      40

      0.750

   

        1.167

   

        

        

        24.4

    (0.750, 1.167)

3.7     88881

   

        0.270

   70

      50

      0.794

   

        1.135

   

        

        

        12.1

    (0.794, 1.135)

3.8     91903

   

        0.263

   70

      50

      0.821

   

        1.105

   

        

        

        18.4

    (0.821, 1.105)

3.9     93457

   

        0.256

   70

      50

      0.834

   

        1.077

   

        

        

        24.4

    (0.834, 1.077)

4       98031

   

        0.250

   70

      60

      0.875

   

        1.050

   

        

        

        12.1

    (0.875, 1.050)

4       101429

  0.250   70

      60

      0.906

   

        1.050

   

        

        

        18.4

    (0.906, 1.050)

4.1     103173

  0.244   70

      60

      0.921

   

        1.024

   

        

        

        24.4

    (0.921, 1.024)

4.2     107353

  0.238   70

      70

      0.959

   

        1.000

   

        

        

        12.1

    (0.959, 1.000)

4.2     111199

  0.238   70

      70

      0.993

   

        1.000

   

        

        

        18.4

    (0.993, 1.000)

4.3     113135

  0.233   70

      70

      1.010

   

        0.977

   

        

        

        24.4

    (1.010, 0.977)

4.4     116795

  0.227   70

      80

      1.043

   

        0.955

   

        

        

        12.1

    (1.043, 0.955)

4.4     121041

  0.227   70

      80

      1.081

   

        0.955

   

        

        

        18.4

    (1.081, 0.955)

4.5     123169

  0.222   70

      80

      1.100

   

        0.933

   

        

        

        24.4

    (1.100, 0.933)

4.5     126363

  0.222   70

      90

      1.128

   

        0.933

   

        

        

        12.1

    (1.128, 0.933)

4.6     130957

  0.217   70

      90

      1.169

   

        0.913

   

        

        

        18.4

    (1.169, 0.913)

4.7     133313

  0.213   70

      90

      1.190

   

        0.894

   

        

        

        24.4

    (1.190, 0.894)



Thanks for any help!











Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005



======================================================

You received this e-mail because you are subscribed 

to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 

from this mailing list send a blank message to 

BLDG-SIM-UNSUBSCRIBE at GARD.COM



===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070404/edda3bfa/attachment.htm 


More information about the Bldg-sim mailing list