[BLDG-SIM] ASHRAE 90.1 - window SHGC
D. Charlie Curcija
curcija at ecs.umass.edu
Mon Apr 9 05:50:01 PDT 2007
International Glazing Database (IGDB), which is part of WINDOW 5.2 program
(windows.lbl.gov) contains several hundred individual glass layers whose
solar transmittance is at or below 0.3, which, as a part of glazing system
and whole fenestration product, would produce SHGC of 0.25 or lower, which
meets ASHRAE 90.1 for all climate zones. The best choice for low SHGC
windows is so called spectrally selective low-e, and there are at least 100
glass products with this type of low-e coating. The cost of these products
is only marginally higher than the cost of clear glass.
I think that you are definitely overlooking something.
Having said that, I do want to state that the use of low SHGC products in
heating dominated climates (anything at or above climate zone 5) is wrong
and is the major flaw of both ASHRAE 90.1 and IECC 2006, particularly for
orientations with potentially high solar gain in the winter, such as South
orientation.
D. Charlie Curcija
Carli, Inc.
18 Tanglewood Rd.
Amherst, MA 01002
Tel: (413) 256-4647
Fax: (413) 256-4823
cell: (413) 575-3487
email: <blocked::mailto:curcija at fenestration.com> curcija at fenestration.com
web: <http://www.fenestration.com/> http://www.fenestration.com
Support open document format as the best way to assure full compatibility
and interoperability!
STATEMENT OF CONFIDENTIALITY
The information contained in this electronic message and any attachments to
this message are intended for the exclusive use of the addressee(s) and may
contain confidential or privileged information. If you are not the intended
recipient, please notify Carli Inc. immediately at either 413-256-4647 or at
home at fenestration.com, and destroy all copies of this message and any
attachments.
_____
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Scott Runyon
Sent: Monday, April 09, 2007 7:52 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] ASHRAE 90.1 - window SHGC
When modeling my design case, I find that most windows cannot achieve the
minimum SHGC suggested in ASHRAE 90.1.
Why would ASHRAE set unattainable minimum values?
Am I overlooking something in ASHRAE 90.1???
Any help would be appreciated.
Thanks,
Scott
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070409/ea6e5eb2/attachment.html
More information about the Bldg-sim
mailing list