Jannes,
   I am not sure which file formats have the soil surface temperature 
in them but TRNSYS is able to read the TMY, TMY2, EnergyPlus, 
International Weather for Energy Calculations (IWEC), Canadian 
Weather for Energy Calculations (CWEC), or user-format data. The most 
extensive data for Europe I believe comes from Meteonorm in TMY2 
format and that is not a format that includes a field for soil 
surface temperature. If you are unable to find a source of soil 
surface temperatures then the two typical solutions that we have used 
are to use the Kasuda correlation (temperature is a function of depth 
and time of year), or a soil surface energy balance. Both are 
available as Types for TRNSYS.
Cheers,
  David

At 02:48 4/12/2007, jacco wrote:

>I would appreciate it if somebody could tell me where i can climate 
>files that incorporate soil surface temperatures for europe and are 
>compatible for TRNSYS 16.
>
>Thanks,
>
>Jannes
>
>
>
>
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070416/08003630/attachment.htm 


More information about the Bldg-sim mailing list