[BLDG-SIM] Baseline for Garage Ventilation using Performance Rating Method, LEED-CS 2.0
gail
gail22 at gmail.com
Fri Apr 20 15:05:23 PDT 2007
I would certainly like to take the Option 2 approach mentioned for all the
projects I'm submitting, but I'm pretty sure it's not allowed:
Table 11.3.1.12 specifically lists garage ventilation fans (and exhaust fans
also) as a "Miscellaneous load". Per the requirements of that section, the
loads "shall be assumed to be identical in the proposed and budget building
design"
This seems to indicate that Option 1 is the only option that would comply
with the requirements of Appendix G.
Best Regards,
Gail Stranske
CTG Energetics, Inc.
On 4/20/07, Bill Talbert <btalbert at aeieng.com> wrote:
>
> Neeraj,
> I would agree that your interpretation and your proposed 'option 2' appear
> to be meeting the requirements of App G. The LEED NC V2.2 Reference Guide
> (refer to EA Credit 1 Calculations for 'Other Systems,' page 182) indicates
> that where specific energy efficiency requirements exist in A90.1, the
> lowest allowable efficiency shall be used for the Baseline. Garage
> ventilation is included in the sample listing of 'other' systems and the fan
> power allowance should apply to that system. Not sure whether LEED CS V2.0has something equivalent.
>
> That said, I am not a LEED reviewer. It would be interesting to hear what
> others think on this as the fan power allowance is likely easy to beat for a
> ventilation only system where system pressure drop is minimal. I would
> expect that the intent of App G may not be to 'credit' these types of
> systems.
> Bill Talbert, AEI
>
> >>> neeraj <near_ej at yahoo.com> 4/20/2007 1:14 PM >>>
> Hi all,
>
> - LEED, Core and Shell V2.0
> - A 300,000 sqft building, 12 stories above ground located in
> Washington DC. The baseline building is System # 8, i.e. VAV fan
> controlled, PIU, all electric heating and cooling.
> - Problem Area -- To determine a correct Baseline: In the proposed
> design, 3 levels of underground parking garage are merely ventilated with
> constant volume fans and they are not equipped with CO/NOx sensors ,
> i.e. they are merely constant volume, SA and EA fans.
> - We know that garage ventilation is not process energy, so it must
> be regulated somehow, right?! Plus, we cannot take credit for energy savings
> from OA ventilation air (according to Appendix G). Now, since this is a
> 'fans only' situation in both the models (no cooling or heating) I have
> assumed the CFM of OA ventilation air must be the same in both cases. Am I
> correct, so far?
> - Using this as a premise, the following two contradicting scenarios
> for an appropriate baseline model can reasonably be thought of:
> 1. Model similar SA and EA CFM as in the "Proposed Building
> Model" with similar fan power kW/CFM, OR
> 2. Model similar SA and EA CFM as in the "Proposed Building
> Model" but calculating the fan power for the OA flow using Section
> G3.1.2.9 of the Informative Appendix G of ASHRAE 90.1-2004.
>
> THE BIG QUESTION(s): Is the second option a valid approach for
> determining fan power (kW/CFM) for the baseline?
> OR
> Is the method only meant for determining (and thus crediting/penalising)
> system supply air fans and not parking garage fans?
>
> Thanks,
> Neeraj
>
>
> ------------------------------
> Ahhh...imagining that irresistible "new car" smell?
> Check out new cars at Yahoo! Autos.<http://us.rd.yahoo.com/evt=48245/*http://autos.yahoo.com/new_cars.html;_ylc=X3oDMTE1YW1jcXJ2BF9TAzk3MTA3MDc2BHNlYwNtYWlsdGFncwRzbGsDbmV3LWNhcnM->
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070420/5ee2c95b/attachment.htm
More information about the Bldg-sim
mailing list