[BLDG-SIM] Doe2 Outputs
Joe Huang
YJHuang at lbl.gov
Tue Jul 11 13:09:47 PDT 2006
Krishna,
You have to be careful in distinguishing Hourly-Reports for LOADS versus SYSTEMS or PLANT. From your description, you seem to be extracting the GLOBAL variables in SYSTEMS, where variable 6 is the current hour of simulation, and 8 is the dry bulb temperature (see DOE-2.1E Supplement, p. A.16). Ground-temperatures in Rankine are available as GLOBAL variable 2 in the LOADS hourly-report (see DOE-2.1E Supplement, p. A.2).
Therefore, you should try moving your HOURLY-REPORT commands from SYSTEMS to LOADS.
Joe Huang
----- Original Message -----
From: Bharath Krishna Karambakkam
To: BLDG-SIM at gard.com
Sent: Tuesday, July 11, 2006 11:41 AM
Subject: [BLDG-SIM] Doe2 Outputs
Hi
I am trying to get the ground temperatures from Doe2.1e. The the Doe2 manual on "Libraries and reports" states that the ground temperature is GLOBAL variable with a variable list number 2. From some examples I have noticed that the we need to add 4 to the stated list number for GLOBAL outputs.
When I specify 8 as the Variable list I get the expected dry bulb temperature as the output. I am assuming that I should specify 6 for the ground temperatures. However I get the current hour as the output instead. Please let me know how I could get the ground temperatures.
Also I am trying to output the BUILDING-LOADS variable list no 10 (building lighting heating loads). When I specify the Variable-Type = BUILDING or even BUILDING-LOADS. I get an error "symbol previously undefined". Please let me know what is to be specified as the VARIABLE-TYPE to get the building loads.
thanks,
Krishna
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060711/042ce42a/attachment.htm
More information about the Bldg-sim
mailing list