[bldg-sim] LEED Credit EA-1 Modeling question
Vikram Sami
VSami at lasarchitect.com
Fri Aug 4 10:49:46 PDT 2006
Mike,
Per the USGBC, LEED NC addresses new buildings and major renovations.
LEED EB is designed to address O&M of existing buildings. If you are
performing a major renovation (which I think you are in this case), you
should use LEED NC. As a rule of thumb a major renovation involves
elements of major HVAC renovation, significant envelope modifications
(adding 2 stories would fall under this I think) and major interior
rehabilitation (Page 24 of the 2.2 reference guide).
I would say you fall under NC. You will probably get less credit for
your energy performance, but I think you can take significant credit in
the MR section for retaining the existing building shell.
Hope this helps
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
________________________________
From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf Of Mike
Tillou
Sent: Friday, August 04, 2006 11:46 AM
To: bldg-sim at gard.com
Subject: [bldg-sim] LEED Credit EA-1 Modeling question
Hi all,
I have aLEED EA-1 question that I am hoping someone has had to deal with
previously.
I am looking at a potential LEED project that involves the extensive
renovation of an existing building and the construction of a new
addition. The existing building is three floors (15,000 sq.ft.) and the
new addition will be two stories (4,000 sq.ft.).
I am wondering how USGBC is currently dealing with projects that
incorporate renovation and addition. At what point is a project still
considered an existing building allowing the use of the Existing
Building savings percentages? I cannot seem to find a discussion about
it in the NC 2.1 User's Manual.
Any advice would be appreciated, thank you.
Mike
Michael Tillou, PE
etc Group, Inc.
PO Box 7, Williamstown, MA 01267
ph. (413) 458-9870 fx. (413) 458-9875
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060804/60f8c8e7/attachment.htm>
More information about the Bldg-sim
mailing list