[BLDG-SIM] Condensing Boilers
Brian Fountain
bfountain at greensim.com
Wed Aug 16 14:44:56 PDT 2006
Natural Resources Canada included a curve for condensing boilers in
their recent EE4 release which is based on the DOE2.1e engine. The
software is free at ee4.com but I don't know the source for the
condensing boiler curves.
They are...
Condensing:
B-HIR-FPLR-COND CURVE-FIT TYPE = QUADRATIC
COEF=(0.00533,0.904,0.09066) ..
Non-condensing:
B-HIR-FPLR-NONCOND CURVE-FIT TYPE = QUADRATIC
COEF=(0.082597,0.996764,-0.079361) ..
Brian Fountain
bfountain at greensim.com
GreenSim
(905)639-6014 - voice | (905)639-0443 - fax
-----Original Message-----
From: BLDG-SIM at GARD.COM [mailto:BLDG-SIM at GARD.COM] On Behalf Of David
S Eldridge
Sent: August 16, 2006 5:03 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] Condensing Boilers
There were a couple of posts out there looking for condensing boiler
curves for DOE2 (Bryce, Doug) - anyone have any luck?
Specifically we're looking at Aerco Benchmark and Gasmaster.
Any help would be appreciated!
Thanks!
David
--------------------------------------------------------------
David S. Eldridge, Jr.
Project Engineer
LEED v2.0 Accredited Professional
Grumman/Butkus Associates
820 Davis St., Suite 300
Evanston, IL 60201
847.328.3555 ext. 224
dse at grummanbutkus.com
-------------------------------------------------------------
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list