[BLDG-SIM] Equest- Central Energy Plant
John Aulbach
jra_sac at yahoo.com
Mon Aug 28 08:26:41 PDT 2006
Hi Scott:
Let's take these in order. And by the way, if you have
used the software only once before, all I will be
describing is in the Detailed Interface Mode, after
you have generally created your building.
Make sure you have done everything in the Wizard Mode
you want. If you make inputs within the Detailed
Interface Mode, going back to a Wizard will erase
these changes:
1) Chiller heat - All heat generating loads are to be
shown in the LOADS portion of your model. If the
chiller is in a particular space (ZONE), you simply
won't put this heat generating load in the space.
You will put the chiller in the PLANT module, and the
program will not care where the chiller is actually
located.
2) In the HVAC section, you can go to the particular
ZONES that will have exhaust fans, and input them
there.
3) Electric Unit heaters - Likewise, on the HVAC
module level, you would input BASEBOARD heating (if
separate from the main HVAC system), or input a Unit
Heater system here as well.
4) Air Rotation Units - I am unfamiliar with this
term. If you mean Fan Filter Units, such as are in
silicon wafer manufacturing, you can simply account
for the electric load in LOADS, unless there is a coil
attached to the unit. Then, I believe, a 4-PIPE
INDUCTION system must be chosen, with the secondary
coil load in the FFUs.
Consult someone who HAS used this software within you
area, as it sounds like you make need help in the
Detailed Interface area.
Hope this gets you started.
--- Scott Runyon <srunyon at rmf.com> wrote:
> For our LEED credit, we are using equest to model a
> central energy
> plant. I am inexperienced in the central energy
> plant area, and I have
> used this software only once before.
>
>
>
> Any help is most appreciated:
>
>
>
> 1) If I am cooling certain portions of the
> plant, how do I make sure
> that the heat generated by the chillers is not
> contributing to that
> building load. I have louvers and a fan venting the
> chiller areas. If
> the building sees the heat by the chillers, then
> obviously, I'm never
> going to achieve my goal of energy reduction in the
> cooling department.
> I've read about setting the tstat for no cooling or
> heating, but am
> unsure if this is the right way to do it and where
> exactly on the
> screens to input this.
>
>
>
> 2) How do I account for exhaust fans in
> specified zones?
>
>
>
> 3) How Do I account for electric unit heaters in
> specified zones?
>
>
>
> 4) How do I account for Air Rotation Units in
> specified zones?
>
>
>
>
>
>
>
> Thanks in advance for your help.
>
>
>
>
>
> Scott Runyon
>
>
>
>
>
>
>
>
=====================================================You
> received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list