[BLDG-SIM] How to simulate VAV systems without cooling coils in eQuest
Peter Alspach
peter.alspach at arup.com
Mon Aug 28 17:44:56 PDT 2006
You can schedule the coil to be off via the availability schedule.
Peter
Peter Alspach, P.E.
Associate
Arup
403 Columbia St., Suite 220
Seattle, WA 98104
T: 206-493-2226
C: 206-816-4902
F: 206-749-0665
E: peter.alspach at arup.com
________________________________
From: BLDG-SIM at GARD.COM [mailto:BLDG-SIM at GARD.COM] On Behalf Of Brandon
Nichols
Sent: Monday, August 28, 2006 5:18 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] How to simulate VAV systems without cooling coils in
eQuest
All,
In the northwest USA we often use VAV systems without cooling for
schools -- 100% outside air economizer cooling, and 'off' for three
months in the summer. The particular system I want to model in eQuest
is the standard VAV with heat recovery, but I can't figure how to either
define it without a cooling coil, or render the cooling coil and chiller
ineffective.
What is the best way to do this?
Thanks
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart Street
Suite 1000
Seattle, WA 98101
www.hargis.biz
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060828/2ac85c93/attachment.htm>
More information about the Bldg-sim
mailing list