Hi Daniel:
So many issues.
Are you allowing the cooling coil(s) to reset to the
warmest zone load? Otherwise, I believe your cooling
coil remains at 55°F.
Nothing to do with the economizer, in my view.
Also, is your thermostat REVERSE-ACTION? There are
those that under stand these controls better than I,
but this allows the VAV box to back open in the
winter, when heating is needed.
Try these items.