I think the easiest (fastest) way to change the glass is to edit .inp file.
Form your email it appears that you used Glass-Type code method .For
example, you can just change the code = 2004 (air gap) to code = 2005 (argon
gap). Toy can see the Glass type description in BDLLIB.dat. You can employ
the same strategy if you used different method of glazing specification.
$ ---------------------------------------------------------
$ Glass Types
$ ---------------------------------------------------------
"Window Type #1 GT" = GLASS-TYPE
TYPE = GLASS-TYPE-CODE
GLASS-TYPE-CODE = "2004"
..
"Window Type #2 GT" = GLASS-TYPE
TYPE = GLASS-TYPE-CODE
GLASS-TYPE-CODE = "2005"
I hope it helps..
Mahabir
..................................................................
Mahabir Bhandari, Ph.D.
Senior Energy Analyst
Carli Inc.
Tel: (413) 256 4647
Fax: (413) 256 4823
Web: <http://www.fenestration.com> www.fenestration.com
_____
From: Scott Runyon [mailto:srunyon at rmf.com]
Sent: Thursday, April 27, 2006 11:20 AM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] Changing window types in detailed edit mode in eQuest
I modeled my entire building and did extra tweaks in the detailed edit mode.
Ive just been informed that the contractor installed different glass than
what was specified, so they are going to keep it.
How do I change glass type from say ¼double pane with air gap to ¼ double
pane with argon gap and not allow it to erase all of my detailed edit work?
I know I have this option at the beginning in the wizard.
When I look at glass types and right click for properties, on the left side
of the screen, it is not descriptive at all. I just see some numbers for the
various properties.
Thanks again for your help.
Scott Runyon
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20060427/3bb9481f/attachment.htm>
More information about the Bldg-sim
mailing list