[BLDG-SIM] WLHPs and Hot Water

Mike Tillou miket at etcgrp.com
Thu Jun 16 19:49:34 PDT 2005


Fred,

DOE 2.2 is capable of using a schedule with a unique value for each hour
of the year.  This allows capabilities similar to the file-load feature
in DOE2.1e.  This is a good way to assign an external load to a
circulation loop.   

For anyone interested I have attached a template for an hourly value
schedule to use in DOE2.2.  It has 53 weeks and 375 days.  The annual
week end-dates are currently set up for 2005.  The holidays are not set
up to match their corresponding day, that would have to be done by the
user.

The schedule I included is a fraction schedule so you will need to
normalize your data similar to the method for making performance curves.
I mentioned one way of doing this in my earlier email.

I recommend making changes within the template first and then importing
the file into your DOE2.2/equest project.

I recently used this to model the performance of an ERV system on a heat
pump   


Regards,

Mike


Michael Tillou, PE
etc Group, Inc.
PO Box 7, Williamstown, MA 01267
ph. (413) 458-9870  fx. (413) 458-9875
www.etcgrp.com
  


-----Original Message-----
From: Fred Porter [mailto:fporter at archenergy.com] 
Sent: Thursday, June 16, 2005 2:21 PM
To: Mike Tillou
Subject: Re: [BLDG-SIM] WLHPs and Hot Water


Mike;
Can DOE2.2 accept a 52 week, 365 separate day schedule now? That would 
be handy for post-processing outputs from other programs, adding in 
metered loads, etc. It used to be limited, but in 2.1 we used the 
function file-read to insert data to a schedule. Do you have an example 
of this method you could share?
Fred

Mike Tillou wrote:

>I was going to recommend the same idea.
>
>Create a boiler on the WLHP and determine the unmet heating load that
>is not met by the heat pumps.  Capture this load in an hourly report 
>and import it into excel (you can create an output report that imports 
>directly into excel).  Find the peak hourly MBTU unmet heating load. 
>Determine the ratio of unmet heating load to peak unmet heating load 
>for each hour of the year.  Create a schedule TYPE=FRACTION using these

>ratio values (52 weeks, 365 days).  In your hot water loop (with the
>boilers) assign a process heating load equal to the peak unmet heating 
>load, use the schedule you created as the process heating schedule.
>
>You can verify this is working right by running hourly reports
>comparing the WLHP boiler load and the process load.  Set the HIR of 
>the WLHP boiler and the kW of the WLHP boiler pump to 0 so that you 
>don't get any unmet heating hours in your air-side systems output (for 
>the heat pump systems).
>
>
>Good Luck,
>
>
>Mike
>
>
>Michael Tillou, PE
>etc Group, Inc.
>PO Box 7, Williamstown, MA 01267
>ph. (413) 458-9870  fx. (413) 458-9875
>www.etcgrp.com
>  
>
>
>-----Original Message-----
>From: postman at gard.com [mailto:postman at gard.com] On Behalf Of John
>Aulbach
>Sent: Thursday, June 16, 2005 12:37 PM
>To: BLDG-SIM at gard.com
>Subject: [BLDG-SIM] WLHPs and Hot Water
>
>
>Wade:
>
>This may the "old fashioned" method, but...
>
>Can't you run the WSHP scenario with a gas fired
>boiler, assuming a 100% boiler efficiency (horrors!),
>and get an 8,760 hourly output on the dynamics of that
>boiler?
>
>Then, input this dynamic heating load (AS A HEATING
>LOAD) into another eQuest run for the rest of your
>loads and main boilers, thus hopefully getting the
>dynamics you need.
>
>At least the theory feels right...
>
>
>__________________________________________________
>Do You Yahoo!?
>Tired of spam?  Yahoo! Mail has the best spam protection around 
>http://mail.yahoo.com
>
>======================================================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
>from this mailing list send a blank message to 
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>====================================================
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe
>from this mailing list send a blank message to 
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>  
>

-- 
Fred W. Porter
Senior Engineer
Architectural Energy Corp.
2540 Frontier Ave. Suite 201
Boulder CO 80301
email: fporter at archenergy.com
fax: 303-444-4304

office: 303-444-4149 x225



===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Hourly Value Schedule 2005.zip
Type: application/x-zip-compressed
Size: 3256 bytes
Desc: Hourly Value Schedule 2005.zip
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20050616/52986348/attachment.bin>


More information about the Bldg-sim mailing list