[BLDG-SIM] dew point and moisture control in walls

Thomas White twhite at glumac.com
Tue Jul 12 15:02:03 PDT 2005


Alpana,
 
You might try MOIST, a free software program you can use to calculate
temperature profiles and dew point in wall assemblies. Check out this URL
for details:
 
 <http://www.bfrl.nist.gov/863/moist.html> www.bfrl.nist.gov/863/moist.html.

 
MOIST is a one-dimensional, steady-state analysis, and there are other
considerations that have to be taken into account when analyzing dew point.
Among them are; seasonal and diurnal variation in wall temperature and RH;
the edge effects of studs, windows and framing; the dynamics of wetting and
drying in a cavity; and how a vapor barrier is used. 
 
...Tom
 
Thomas J. White, P.E.
Lead Engineer, Energy Services

 <http://www.glumac.com/>  
  _____  

320 SW Washington, Suite 200
Portland, OR 97204-2640
T.  503.227.5280  F. 503.274.7674  D. 503-345-6246

Thinking. Inside the building.
 <http://www.glumac.com/> http://www.glumac.com
 
 
-----Original Message-----
From: Alpana Jain [mailto:ajain at setty.com]
Sent: Tuesday, July 12, 2005 2:19 PM
To: BLDG-SIM at GARD.COM
Subject: [BLDG-SIM] dew point and moisture control in walls



Hi,

 

I was wondering if there is some way of modeling the effect and extent of
the vapor pressure, dew point and condensation within walls? 

 

Alpana



=====================================================You received this
e-mail because you are subscribed 

to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 

from this mailing list send a blank message to 

BLDG-SIM-UNSUBSCRIBE at GARD.COM


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20050712/4774a690/attachment.htm>


More information about the Bldg-sim mailing list