Your conditioned and plenum spaces would have to be modified in the
"Detailed" mode such that any roof with skylights is attached to the
conditioned space and not the plenum space.  The plenum would then have
interior walls as boundaries separating the plenum from the conditioned
space with the conditioned space defined as the "space next to".

Good luck,

Sheila Sagerer
Energy Engineer, LEED AP
Energy Opportunities, Inc
PH: 717-880-9069
Fax: 717-291-9497


-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com]On Behalf Of Mohit Mehta
Sent: Friday, January 21, 2005 12:18 PM
To: bldg-sim at gard.com
Subject: [bldg-sim] eQUEST


I have a relatively tall space, which has a plenum defined by an
internal ceiling. But this space also has large strip skylights over
parts of it [no plenum under skylights only].
If I define a plenum -
Will skylight loads be registering accurately in the main space below
[how does eQUEST distribute the loads]?
Will it have accurate read of daylight distribution?