[BLDG-SIM] Steam-Turbine Drive Centrigugal LiquidChillers - UPDATE
Chris Jones
cj at cr-jay.ca
Thu Nov 18 06:41:39 PST 2004
District steam is not always waste energy from a power plant. In the case
that district steam is just for heating and cooling, then the ASHRAE 90.1
states correctly that the heating and/or cooling should be modelled as
purchased using the applicable rate. For situations were the building uses
steam that can't be used by the power plant I would suggest that the
proposed would only get credit if the overall steam efficiency (work out/
fuel in) is greater than 75% AFUE. This is the budget building
perscriptive requirement for steam boilers. LEED should not give credit
for using a convenient heat/cool source if that source is inefficient overall.
At 15:24 12/11/2004, Varkie Thomas wrote:
>
>At the end of this message is the part load performance of steam turbine
>chillers. As you can see from the response from Rob Firnstein of York,
>energy software developers can incorporate this data into their programs.
>
>Steam turbine chillers have recently been specified for buildings in
>NYC. ConEd has low summer rates for steam. Cities like Boston,
>Minneapolis and Philadelphia also provide district steam. Since district
>steam is waste energy from a power plant perhaps there should be LEED
>credits for using this waste energy although the ECB method might show
>higher costs over electric centrifugal.
>
>Varkie Thomas
>
>
>-----Original Message-----
>From: Robert Firnstein [mailto:robert.firnstein at york.com]
>Sent: Thursday, November 11, 2004 3:20 PM
>To: Varkie Thomas
>Subject: RE: Steam Turbine YK rating
>
>Varkie,
>
>Feel free to forward on the information. Recently, York re-designed the
>software for selecting our steam turbine chillers so that we now have
>greater capability to pair compressors and steam turbines for optimum
>performance. If you are interested in seeing any generic selections for
>additional chillers please let me know.
>
>Regards,
>
>Rob Firnstein
>Sales Engineer
>York International - Chicago
>PH:(847)493-6124 FX:(847)759-0676
>
>Part Load Performance at Condenser Water Temperatures (CWT)
>Constant Speed Operation at 4500 RPM, 125 PSIG D&S Steam Supply, Producing
>41oF Chilled Water
> RCLWT = Refrigerant Condenser Leaving Water Temperature
>CWT %
>Load 100% 90% 80% 70% 60% 50% 40%
>30% 20% 15%
> Tons 1800 1620 1440 1260
> 1080 900 720 540 360 270
>85oF BHP 1,378.0 1,210.6 1,058.2 923.6
>802.4 690.4 583.9 - - - - - - - - -
> Lbs/Hr 17,873 15,919 13,884 12,210
> 10,744 9,383 8,029 - - - - - - - - -
> Lbs/TR-Hr 9.93 9.83 9.64 9.69
> 9.95 10.43 11.15 - - - - - - - - -
> RCLWT
> oF 94.33 93.38 92.43 91.50 90.57 89.67
> 88.76 - - - - - - - - -
>75oF BHP 1,182.8 1,043.2 918.6 808.1
>706.6 611.3 519.1 427.5 335.3 307.1
> Lbs/Hr 15,069 13,395 11,832 10,497
> 9,264 8,106 6,982 5,912 4,781 4,453
> Lbs/TR-Hr 8.37 8.27 8.22 8.33
> 8.58 9.01 9.70 10.95 13.28 16.49
> RCLWT
> oF 84.14 83.20 82.28 81.37 80.47 79.58
> 78.69 77.80 76.92 76.34
>65oF BHP 1,035.7 921.1 817.9 723.4
>634.6 550.3 467.6 384.3 299.7 264.8
> Lbs/Hr 13,008 11,633 10,412 9,332
> 8,180 7,215 6,256 5,292 4,307 3,901
> Lbs/TR-Hr 7.23 7.18 7.23 7.41
> 7.57 8.02 8.69 9.80 11.96 14.45
> RCLWT
> oF 73.99 73.08 72.18 71.28 70.40 69.52
> 68.64 67.76 66.88 66.42
>55oF BHP 926.6 828.4 738.3 654.3
>574.3 496.1 418.8 339.9 259.5 220.2
> Lbs/Hr 11,527 10,405 9,369 8,408
> 7,485 6,588 5,691 4,776 3,834 3,365
> Lbs/TR-Hr 6.40 6.42 6.51 6.67
> 6.93 7.32 7.90 8.84 10.65 12.46
> RCLWT
> oF 63.87 62.98 62.09 61.21 60.34 59.46
> 58.59 57.72 56.84 56.43
>
>
>
>
>
>You received this e-mail because you are subscribed
>to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
>from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at GARD.COM
Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20041118/8affc661/attachment.htm>
More information about the Bldg-sim
mailing list