Smita Chandra smita at swinter.com
Tue Dec 21 08:23:08 PST 2004


Dear Gary Zeng,

Usually you can simplify the wave into a few rectangles/trapezoids.  A few 
degrees difference in tilt will not affect your results to any significant 
degree.  What matters is (1) the tilt of the roof surface, and (2) the 
surface area of the roof; the first affects solar gain, the second heat 
transfer.  As long as your simplification matches these two criteria 
reasonably well, your results should be reasonable as well.

Sincerely,
Smita

At 07:43 AM 12/18/2004 Saturday, you wrote:
>zeng-yi at etang.com

Dear guys:
now I am using equest3.5 in a energy simulation project.A big barrier is 
the wave shaped roof,whicn i did not know how to model it. I would like to 
know how i can create a simulation model in equest or other visual tool 
like VisualDOE.
it is urgent to me and any help is greatly appreciated.
u can reach me directly by zeng-yi at etang.com or reply this message.



Smita Chandra
Energy Analyst
M. Arch., LEED accredited professional
smita at swinter.com
Phone Extension 295

Steven Winter Associates, Inc.
50, Washington St
Norwalk, CT 06854
(203) 857-0200 (Phone)
(203) 852-0741 (Fax)
www.swinter.com


======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20041221/b4beba97/attachment.htm>


More information about the Bldg-sim mailing list