[BLDG-SIM] Modeling 100% OA VAV systems in eQuest

Joe Hager jhager at dmiinc.com
Mon Aug 30 09:15:41 PDT 2004


MessageI recently encountered this same issue.  I found out if I switched the system type to a Powered Induction Unit that the model would have variable flow.  Another place to look at is your thermostat type, some systems default to either proportional or reverse action which effects how VAV boxes respond to heating and cooling loads.

Joe Hager
DMI
450 Lexington St.
Newton, MA 02466
voice: 617-527-1525 ext. 102
fax: 617-527-6606 
  ----- Original Message ----- 
  From: Keir Howell 
  To: BLDG-SIM at gard.com 
  Sent: Monday, August 30, 2004 11:25 AM
  Subject: [BLDG-SIM] Modeling 100% OA VAV systems in eQuest


  Hello. Whenever I try to model a VAV system with 100% OA in eQuest, I end up with a constant volume system. It seems to be multiplying the Minimum OA Ratio (which I have set at 1.00) by the design air flow, rather than the hourly air flow, even though I have set the Minimum OA Method to "Fraction of Hourly Flow". As far as I know, I have not set any other variables (such as zonal settings) that might override the system settings. Please help. Thanks,

  Keir Howell
  Bluestone Energy Services, Inc.
  phone:    781-356-8865
  fax:    781-356-8864

==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM


===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040830/bbfd3860/attachment.htm>


More information about the Bldg-sim mailing list