[BLDG-SIM] Curtain wall frames and fenestration area
Mike Tillou
miket at etcgrp.com
Mon Apr 12 07:44:01 PDT 2004
Renee,
The easiest way to do this is to use a single window on each wall. Calculate the percentage of window area that is actually frame and then adjust the frame-width to account for the increase. You may end up with a window frame width that is 12 inches or bigger (if the wall is large enough). With a little ingenuity you can write some BDL code that will automatically calculate the window width, frame width and x position of the window on the wall so you don't get any cautions or warnings. .
Michael Tillou, PE
etc Group, Inc.
PO Box 749, North Adams, MA 01247
Ph. (413) 458-9870 Mbl. (413) 652-1087 www.etcgrp.com <http://www.etcgrp.com>
________________________________
From: postman at gard.com on behalf of Azerbegi, Renee
Sent: Mon 4/12/2004 7:44 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Curtain wall frames and fenestration area
Greetings,
I am modeling a high-rise building in eQuest which has a significant amount of fenestration as curtain wall. This curtain wall, like many curtain walls, has metal frames around many small panes of glass that make up the total curtain wall. My question is, how do you treat the frames and the fenestration area? If I model each small pane of glass and add the exact frame, this would probably overwhelm DOE2 due to the huge number of small windows. If I model the glass as one big window, then is it correct to just add the total width of the frame to each of these large windows? Also, some of these curtain wall panes have fins to complicate things, so if I do one big glass pane, then adding the fins would make huge fins on either side of the glass. If you have dealt with modeling curtain walls, as probably many of you have, please let me know how you have dealt with these issues.
Thank you,
Renee
Renee Azerbegi
RMH Group
303-239-0909x641
This email was scanned by SC E-mail Anti-Virus Agent at 7:44:05 AM 4/12/2004 the RMH Group, Inc.
---->
This email and any files transmitted with it are confidential and intended solely for the use
of the individual or entity to whom they are addressed. If you have received this email in
error please immediately notify the RMH Group Inc. by telephone at (303) 239-0909 or
send a reply to Services at RMHgroup.com with "Return to sender" in the subject line.
<----
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20040412/b57c67ab/attachment.htm>
More information about the Bldg-sim
mailing list