Question answered...
-----Original Message-----
From: Jeff Hirsch [mailto:Jeff.Hirsch at DOE2.com]
Sent: Thursday, August 07, 2003 4:17 PM
To: Aulbach, John
Subject: Re: [bldg-sim] Another DOE-2 question..
LS-F (and LS-E), you must remember, list the load components for a NET
heating or cooling load;
thus a reduction of lighting load will probably cause a change in the hours
of net heating and cooling
load for both the spaces and the whole building ... thus, when you then look
at the occ/equ contributions
to the net load, they may change greatly even though the total occ/equ loads
are very close to the same
(not exactly as we are talking about net load to the spaces when some goes
out the windows and walls
via direct radiation to the surface then conduction out the other side.)
---
Jeff Hirsch
James J. Hirsch & Associates
Building Performance Analysis Software & Consulting
12185 Presilla Road
Camarillo, CA 93012-9243 USA
phone: (805) 553-9000
fax: (805) 532-2401
email: Jeff.Hirsch at DOE2.com <mailto:Jeff.Hirsch at DOE2.com>
web: http://DOE2.com <http://DOE2.com>
----- Original Message -----
From: Aulbach, John <mailto:JAulbach at semprasolutions.com>
To: bldg-sim at gard.com <mailto:bldg-sim at gard.com>
Sent: Thursday, August 07, 2003 12:40 PM
Subject: [bldg-sim] Another DOE-2 question..
By the way, I resolved my previous OSA question. Thanks to all who
contributed..
Same school. A Base Case and a Retrofit Case.
Base Case is a central plant with 20 some air units, fixed economizer.
Retrofit Case are individual Air heat Pumps, WITH economizer. Also a
Lighting Retrofit (same operating hours).
The LS-F report shows a DOUBLING of the contribution of Occupancy AND
Equipment on the load. Same building envelope, occupancy and equipment
density, same operating schedules. And the program does NOT yet know that
the SYSTEM has changed.
Any ideas?
John R. Aulbach, PE, CEM
Project Engineer
Sempra Energy Solutions
555 West Fifth Street
Mail Location 27F3
Los Angeles, CA 90013
Tel: (213) 244-8551 Cell (213) 219-4875
"Sempra Energy Solutions is not the same company as SDG&E/ SoCalGas, the
Utilities. Sempra Energy Solutions is not regulated by the California
Public Utilities Commission, and you do not have to buy Sempra Energy
Solutions products or services to continue to receive quality regulated
service from the Utilities."
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20030807/1b0465bd/attachment.htm>
More information about the Bldg-sim
mailing list