[BLDG-SIM] Screw chiller performance curves
Alec Stevens
astevens at dmiinc.com
Wed Jan 16 13:49:36 PST 2002
Steve,
Thanks for this update.
Two additional questions:
1) will the new version of DOE2.2 that models the screw chillers and the VFD chillers be incorporated into PowerDOE? (maybe a question for Jeff Hirsch)
2) are there / will there be any default curves for air-cooled screw chillers? I have been trying to model this without much success so far. I created my own curves, but the results don't appear to make sense. When I created an output report, the modified values of EIR based on my curves made good sense, but the chiller kW that is being shown makes no sense at all. I haven't finished debugging this yet, but wonder if anyone has any suggestions.
Sincerely,
Alec Stevens
DMI
p: 617-527-1525x105
f: 617-527-6606
e: astevens at dmiinc.com
----- Original Message -----
From: Steve Gates
To: BLDG-SIM at gard.com
Sent: Wednesday, January 16, 2002 3:31 PM
Subject: [BLDG-SIM] Screw chiller performance curves
James Hirsch & Associates is currently implementing new chiller algorithms in DOE-2, and defaults performance curves for screw chillers will be included.
For both reciprocating and screw chillers, the program will use different performance curves depending on the number of compressors in the machine. The program will also model centrifugal chillers with variable-speed drives. Since some of these curves utilize new types of CURVE-FITS, they require a new version of DOE-2.2 which won't be released for another month or two.
In the meantime, for current versions of DOE-2.2, the following models a water-cooled screw:
"ScrewH2O-Cap-fCHWT&LCT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = DATA
IN-TEMP1 = ( 44.0, 44.0, 44.0, 44.0, 44.0, $ CHW T
48.0, 48.0, 48.0, 48.0, 48.0,
52.0, 52.0, 52.0, 52.0, 51.0,
40.0, 40.0, 40.0, 40.0, 40.0)
IN-TEMP2 = ( 85.0, 75.0, 70.0, 95.0, 100., $ ECT
85.0, 75.0, 70.0, 95.0, 100.,
85.0, 75.0, 70.0, 95.0, 100.,
85.0, 75.0, 70.0, 95.0, 100.)
OUTPUT = ( 1.00, 1.07, 1.10, 0.92, 0.89, $ Capacity ratio
1.09, 1.16, 1.18, 1.00, 0.96,
1.18, 1.24, 1.26, 1.09, 1.05,
0.92, 0.99, 1.02, 0.85, 0.83) ..
"ScrewH2O-EIR-fCHWT&LCT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = DATA
IN-TEMP1 = ( 44.0, 44.0, 44.0, 44.0, 44.0, $ CHW T
48.0, 48.0, 48.0, 48.0, 48.0,
52.0, 52.0, 52.0, 52.0, 51.0,
40.0, 40.0, 40.0, 40.0, 40.0)
IN-TEMP2 = ( 85.0, 75.0, 70.0, 95.0, 100., $ ECT
85.0, 75.0, 70.0, 95.0, 100.,
85.0, 75.0, 70.0, 95.0, 100.,
85.0, 75.0, 70.0, 95.0, 100.)
OUTPUT = ( 1.00, 0.85, 0.78, 1.20, 1.31, $ EIR ratio
0.94, 0.81, 0.74, 1.13, 1.24,
0.90, 0.77, 0.71, 1.07, 1.17,
1.06, 0.89, 0.82, 1.27, 1.39) ..
$ Two circuits, one compressor/circuit
"ScrewH2O-EIR-fPLR&dT-1Comp/Ckt" = CURVE-FIT
TYPE = QUADRATIC
INPUT-TYPE = DATA
INPUT = ( 1.00, 0.75, 0.50, 0.25, 0.10)
OUTPUT = ( 1.00, .906, .538, .332, .141) ..
$ Two circuits, two compressors/circuit
"ScrewH2O-EIR-fPLR&dT-2Comp/Ckt" = CURVE-FIT
TYPE = QUADRATIC
INPUT-TYPE = DATA
INPUT = ( 1.00, 0.75, 0.50, 0.25, 0.10)
OUTPUT = ( 1.00, .842, .664, .289, .151) ..
"A Generic Screw Chiller" = CHILLER
TYPE = ELEC-HERM-REC
ELEC-INPUT-RATIO = .202
CAPACITY-FT = "ScrewH2O-Cap-fCHWT&LCT"
EIR-FT = "ScrewH2O-EIR-fCHWT&LCT"
EIR-FPLR = "ScrewH2O-EIR-fPLR&dT-1Comp/Ckt"
etc.
..
Hope this helps!
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20020116/4ab2d877/attachment.htm>
More information about the Bldg-sim
mailing list