[BLDG-SIM] Barrow, Alaska weather file
Steve Gates
stvgates at pacbell.net
Fri Apr 12 14:26:19 PDT 2002
Drury and Jason are correct; this is a DOE-2 bug (all versions) that does not allow the program to simulate latitudes at or above the arctic circle (also true in the Southern hemisphere). Drury's suggestion should allow you to get around the problem.
DOE-2.2, Version 41 and later fixes this problem. The program now also recognizes that sun angles can change radically from one month to the next in high latitudes (especially spring/fall, even in more temperate latitudes), and will recalculate shading angles more often than once per month when it encounters this situation. Users of DOE-2.2 should download Version 41a from the FTP site.
eQUEST is expected will contain this fix sometime this quarter. We are considering porting this fix into DOE-2.1e as well, but have not yet done so.
----- Original Message -----
From: Drury.Crawley at EE.DOE.GOV
To: BLDG-SIM at gard.com
Sent: Friday, April 12, 2002 12:18 PM
Subject: [BLDG-SIM] Barrow, Alaska weather file
The easy fix is to move the location latitude
slightly below the arctic circle. DOE-2.1E won't
bomb then.
"Jason Glazer"
<jglazer at gard. To: BLDG-SIM at gard.com
com> cc:
Sent by: Subject: [BLDG-SIM] Barrow, Alaska
postman at gard.c weather file
om
04/12/2002
02:39 PM
Please respond
to jglazer
Barrow, Alaska is above the arctic circle so (many? all?)
DOE-2.1e versions will crash. It is a bug that has been
around a while.
Jason
On 12 Apr 2002 at 10:56, Tanmay wrote:
> Has anyone successfully used the Barrow, Alaska TMY2
> weather file for DOE-2 simulations? I've tried using the
> file from a couple of different sources, and the file
> appears to be corrupt everywhere. It crashes the simulation
> after BDL.
>
> Does anyone have another DOE-2 weather file for Barrow,
> Alaska?
>
> Thanks,
>
>
> Tanmay Tathagat
>
>
>
> ======================================================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To unsubscribe from
> this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
=========================================================
Jason Glazer, P.E. mailto:jglazer at gard.com 847 698 5686
GARD Analytics - http://www.gard.com/
1028 Busse Highway, Park Ridge, IL 60068
Building Energy Simulation and Analysis
List Administrator for 90.1, GPC18 and BLDG-SIM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20020412/bdb1aa62/attachment.htm>
More information about the Bldg-sim
mailing list