[Bldg-rate] LEED Review Comment: Spaces served by Unit Heaters
Kevin Kyte
KKyte at watts-ae.com
Wed Jan 7 08:44:17 PST 2015
Sorry for the cross-postings.
3. It is unclear how the spaces served by unit heaters have been modeled in the Baseline model. Provide a clarification narrative on the modeling methodology with regards to system sizing, fan power, and capacities.
It is unclear why this comment is stated for a project pursuing version 2.2. A space served by a unit heater must be modeled with cooling identical to its system modeled in baseline per ASHRAE 90.1-2004 Table G3.1.10.d. A unit heater is not acceptable criteria for exception to G3.1.1. Therefore if a building baseline HVAC system type is regarding as VAV then spaces served by unit heaters must also have a VAV baseline HVAC system type.
It is understood that ASHRAE 90.1-2010 contains an exception to Table G3.1.10.d and that G3.1.1 contains exception e. However, this should not apply to V2.2.
Am I missing something again or is this a plug-in comment from later versions?
Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-rate-onebuilding.org/attachments/20150107/def22c7d/attachment-0001.htm>
More information about the Bldg-rate
mailing list