[Bldg-rate] [Bldg-sim] PSZ-AC
Paul Riemer
Paul.Riemer at dunhameng.com
Fri Sep 5 10:48:19 PDT 2008
Carol,
I agree mostly but I would reverse your last statement to say to create one PSZ-AC or PSZ-HP per thermal zone. Remember in Appendix G, the modeler does not get to decide the HVAC zoning. Per Table G3.1.8, the zoning is the design zoning if it exists or a prescribed zoning of core & 15' perimeter zones by glazed orientation etc...
(If your proposed is multiple zone VAV and your baseline is going to be PSZ-AC or PSZ-HP, do a little reading and thinking before choosing the PSZ system type in eQUEST/DOE-2.2 or you might have many years and much pain as a great teacher on one project).
I have always assumed that it would be technically wrong to put more than one zone on your PSZ-AC or PSZ-HP but I guess I can not cite a code section to prove it. Can anyone else or other opinions?
Paul Riemer
-----Original Message-----
From: Carol Gardner [mailto:gems at spiritone.com]
Sent: Sunday, September 21, 2008 11:39 AM
To: Paul Riemer
Cc: bldg-sim at lists.onebuilding.org; bldg-rate at lists.onebuilding.org
Subject: Re: [Bldg-sim] PSZ-AC
I think there's some confusion about spaces vs zones. A thermal zone can
have many spaces and be served by one packaged single zone system (PSZ).
A multizone system is one system serves each space/zone. While you can
attach more than one thermal zone to a PSZ system and not be technically
wrong to do so you will have the devil to pay because of the Control
Zone that you have to specify in eQUEST. It is almost impossible to
specify a control zone that won't create hours loads not met for the
other spaces in your output. There is a way around that, only specify a
heating/cooling schedule for the control zone and leave the others
blank, but it is far better to just create one thermal zone for each
PSZ: that meets all the requirements related to ASHRAE, LEED, god, etc.
I hope this helps. Many years and much pain have been a great teacher.
Carol
Paul Riemer wrote:
> I would be leery about combining zones as the baseline cooling
> efficiency, fan power, and economizer should be set by each unit's
> tonnage, cfm, and sf respectively. Further it is not your design cfm &
> tonnage but rather the baseline autosized cfm & tonnage.
> Also be sure you know your software because some programs will allow
> you to but more than one zone on a "single zone system" and then model
> no control or reheat on the secondary zones, either of which be
> outside the intent of Appendix G's system 3.
>
> ------------------------------------------------------------------------
> *From:* bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of
> *Kendra Tupper
> *Sent:* Friday, September 05, 2008 9:34 AM
> *To:* Dan Russell; Eric Youngson; bldg-sim at lists.onebuilding.org
> *Cc:* bldg-rate at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] PSZ-AC
>
> I agree with Dan. The 90.1 User's Manual is a bit more clear on
> this subject, and references that a PSZ unit is created for each
> thermal zone.
>
> ------------------------------------------------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Dan
> Russell
> *Sent:* Thursday, September 04, 2008 4:12 PM
> *To:* Eric Youngson; bldg-sim at lists.onebuilding.org
> *Cc:* bldg-rate at lists.onebuilding.org
> *Subject:* Re: [Bldg-sim] PSZ-AC
>
> Eric,
>
> I understand System 3 (PSZ-AC) to be a standard packaged rooftop
> that may serve multiple "spaces", but only serves a single
> "thermal zone". In other words, there is only one thermostat that
> controls the entire unit.
>
> Your baseline should have a separate PSZ-AC for each thermal zone
> depicted by your HVAC drawings. Note that adjacent thermal zones
> with similar load characteristics (light/equip gain, people count,
> exterior exposure, etc.) may be lumped into a single thermal zone
> for modeling purposes (i.e. less zones = simpler model).
>
> Hope that helps.
>
> Dan Russell, EIT
>
> cid:image001.jpg at 01C840A4.E711B250
>
> *From:* bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of
> *Eric Youngson
> *Sent:* Thursday, September 04, 2008 3:33 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Cc:* bldg-rate at lists.onebuilding.org
> *Subject:* [Bldg-sim] PSZ-AC
>
> Sim List,
>
> ASHRAE system 3 is, Packaged Single Zone Air Conditioner (PSZ-AC).
> The description of PSZ-AC says, "Packaged rooftop air
> conditioner". I assume that this means a single unit serving
> multiple zones. This doesn't seem to make sense since the name
> contains the phrase 'single zone'.
>
> I have a building with baseline system 3, PSZ-AC and I'm not sure
> how to apply this system. The proposed building has a variety of
> systems. Should I have a system per zone or a single unit for the
> building?
>
> Thanks
>
> http://www.pae-engineers.com/images/PAElogobug.gif
> <http://console.mxlogic.com/redir/?bbBT6rTpdFLLLnuusdw0BJYLY2cEvYqsLxKVKVIwuwhbQAGn8lrxrW0E-l9QWIf8dOfgB0zM04SOqen6mjqaqtT4TSnDPqq9I5-Aq83iScDE4iZ9aCBQQg1oo0AK82hKvxYY1NJ4SyrjvvuKYYYrkV-8>
>
>
>
> *Eric Youngson *
>
>
>
> http://www.pae-engineers.com/images/spc1blk.gif
>
>
>
> *PAE Consulting Engineers, Inc.*
>
>
>
> http://www.pae-engineers.com/images/spc1blk.gif
>
>
>
> 503.226.2921 Main
> 503.542.0567 Direct
> 503.226.2930 Fax
> ericy at pae-engineers.com
>
> Mechanical
>
>
>
> 808 SW Third Avenue - Suite 300
> Portland, OR 97204-2426
> www.pae-engineers.com
>
> inspire interpret integrate
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Bldg-rate
mailing list