Kendra,
You are right. The user-guide specifies on page G-27:
Systems 3 and 4 are single zone
packages with either gas or heat pump
heating. Whether the baseline building
system has an economizer depends on the
area served by the system, whether the
zone served is a perimeter or an interior
zone, and climate. Table G3.1.2.6A gives
the floor area served by the system, above
which an economizer is needed. For the
purposes of defining interior and
perimeter zones, any thermal zone that
has more than half of its floor area located
more than 15 ft from an exterior wall is to
be considered an interior zone, otherwise,
it is a perimeter zone.
Thanks!
Eric
From: Kendra Tupper [mailto:ktupper at rmi.org]
Sent: Friday, September 05, 2008 7:34 AM
To: Dan Russell; Eric Youngson; bldg-sim at lists.onebuilding.org
Cc: bldg-rate at lists.onebuilding.org
Subject: RE: [Bldg-sim] PSZ-AC
I agree with Dan. The 90.1 User's Manual is a bit more clear on this
subject, and references that a PSZ unit is created for each thermal
zone.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Russell
Sent: Thursday, September 04, 2008 4:12 PM
To: Eric Youngson; bldg-sim at lists.onebuilding.org
Cc: bldg-rate at lists.onebuilding.org
Subject: Re: [Bldg-sim] PSZ-AC
Eric,
I understand System 3 (PSZ-AC) to be a standard packaged rooftop that
may serve multiple "spaces", but only serves a single "thermal zone".
In other words, there is only one thermostat that controls the entire
unit.
Your baseline should have a separate PSZ-AC for each thermal zone
depicted by your HVAC drawings. Note that adjacent thermal zones with
similar load characteristics (light/equip gain, people count, exterior
exposure, etc.) may be lumped into a single thermal zone for modeling
purposes (i.e. less zones = simpler model).
Hope that helps.
Dan Russell, EIT
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eric
Youngson
Sent: Thursday, September 04, 2008 3:33 PM
To: bldg-sim at lists.onebuilding.org
Cc: bldg-rate at lists.onebuilding.org
Subject: [Bldg-sim] PSZ-AC
Sim List,
ASHRAE system 3 is, Packaged Single Zone Air Conditioner
(PSZ-AC). The description of PSZ-AC says, "Packaged rooftop air
conditioner". I assume that this means a single unit serving multiple
zones. This doesn't seem to make sense since the name contains the
phrase 'single zone'.
I have a building with baseline system 3, PSZ-AC and I'm
not sure how to apply this system. The proposed building has a variety
of systems. Should I have a system per zone or a single unit for the
building?
Thanks
<http://www.pae-engineers.com/>
Eric Youngson
PAE Consulting Engineers, Inc.
503.226.2921 Main
503.542.0567 Direct
503.226.2930 Fax
ericy at pae-engineers.com
Mechanical
808 SW Third Avenue - Suite 300
Portland, OR 97204-2426
www.pae-engineers.com
inspire interpret integrate
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-rate-onebuilding.org/attachments/20080905/63835c07/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7994 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-rate-onebuilding.org/attachments/20080905/63835c07/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2029 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-rate-onebuilding.org/attachments/20080905/63835c07/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 126 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-rate-onebuilding.org/attachments/20080905/63835c07/attachment-0001.gif>
More information about the Bldg-rate
mailing list