[Equest-users] LEED review comments for System 5 heating source
Paul Diglio
paul.diglio at sbcglobal.net
Thu Jun 30 14:48:08 PDT 2011
Lan:
90.1-2007 requires a system 5 with a fossil fuel hot water boiler as you have
modeled, but in 90.1-2007 Table G3.1 Number 10 HVAC Systems Base Building
Performance column it states that you need to meet any system-specific
requirements in Section G3.1.3.
In G3.1.3.2, it states that for system 5, the boiler plant shall use the same
fuel as the proposed design, which in your case is electric resistance and
compressor heat pump energy. I would model electric hot water boilers.
Paul Diglio
________________________________
From: "Li, Lan" <lli at sbmce.com>
To: equest-users at lists.onebuilding.org
Sent: Thu, June 30, 2011 4:24:27 PM
Subject: [Equest-users] LEED review comments for System 5 heating source
Dear eQuesters,
I just got LEED review comments for my project. Our proposed design is VRF
system with roof top unit providing ventilation air. Roof top unit is using gas
as heating source. There are misc. elec. heaters in the building for places like
entries. I interpreted my building heating source as “electric hybrid” and used
hot water fossil fuel boiler as my base design. The comments I got read as the
follows:
Section 1.1.A of the form indicates that the primary heating source is fossil
fuel. However, the electric heating energy use reported in Table EAp2-5 for the
Proposed Case exceeds the fossil fuel heating energy use. Please verify that the
correct heating source has been selected. If electric heating is the primary
heating source, please change the Baseline system type accordingly. Provide
updated simulation results and a revised Prerequisite Form as necessary.
I couldn’t find an official definition either on LEED reference book or 90.1.
What is your take on this?
Your input is highly appreciated! Thank you very much!
Lan
Lan Li, PE, LEED AP BD+C
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Fax: (330) 896-9180
Cell:(330) 904-6292
lli at sbmce.com
www.sbmce.com
ColumbusOffice (614) 448-1498
üPlease consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally
privileged. If you are not an intended recipient or an authorized representative
of an intended recipient, you are prohibited from using, copying or distributing
the information in this e-mail or its attachments. If you have received this
e-mail in error, please notify the sender immediately by return e-mail and
delete all copies of this message and any attachments.
Thank you
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110630/c0cd9d03/attachment.htm>
More information about the Equest-users
mailing list