[Equest-users] Chiller Baseline Methodology

MatthewRLarson at Eaton.com MatthewRLarson at Eaton.com
Tue Jun 28 14:56:25 PDT 2011


Javed,

 

The guideline was created to create the chiller plant defined by ASHRAE
90.1 Appendix G which is used for LEED modeling and accepted by USGBC.
This information is located in Appendix G Section G3.1.3.7 through
G3.1.3.10, which if you don't have a copy of Appendix G, it is a
must-have.  It basically states for plants greater than 300 tons, you
will have variable speed pumps on the secondary loop instead of the
pumps riding the pump curve.  You will also have 2 chillers for plants
>300 tons.  This is all stated in the Appendix G document.  Hope this
helps!

 

Thanks,

 

Matthew Larson, LEED AP BD+C
Project Engineer

Energy Solutions Group

E M C Engineers, Inc.
Eaton's Electrical Services & Systems 
143 Union Blvd, Suite 350
Lakewood, CO 80228
tel: +1 303 328-3419
mobile: +1 303 668-2511
fax: +1 303 974-1239

MatthewRLarson at Eaton.com 
www.eaton.com/energysolutions  

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of javed
iqbal
Sent: Monday, June 27, 2011 10:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chiller Baseline Methodology

 

Hi All,

             I have found this guideline for Baseline Chiller Plant
Modeling for capacity <300 TR. I just wanted to know is it acceptable by
USGBC? What will be the methodology for Plant >300 TR?

Please find the parent link for this attachment.

http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2010
-November/006884.html

Thanks

-- 


Javed Iqbal, LEED AP, CEA
Project Manager   

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/f5dcb0ab/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 39998 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110628/f5dcb0ab/attachment.jpeg>


More information about the Equest-users mailing list