[Equest-users] Boiler HIR
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Tue Jun 21 22:23:40 PDT 2011
Hi Omer,
based on my recent (cited) example from the Reviewer's comments on the
baseline natural draft boiler...this is what I learned from my model and
experience going through this last week for my review comments...
- Natural draft boiler should not show any electric energy use; therefore
the primary equipment efficiency would be an HIR value of 80% or (1/80%) =
1.25 input value. The EIR variable in eQuest defaults to something
relatively small like 0.4% energy use in my recentl model, but the reviewer
didn't even like to see such a negligible amount of "nothing" in the EIR
value which resulted in a very small output number listed under the electric
Spacy Heating end use category.
- When I "zeroed" out the EIR input variable (default or not) this
removed all traces of electric space heating associated with my model.
- Therefore; for your baseline boiler you will need to use HIR = 1.25,
EIR = 0.0 and then model your proposed boiler design as designed so that you
may take advantage of any furhter potential energy savings if you want.
-
Does this help you? Cheers,
Pasha
2011/6/21 Ömer Moltay <omoltay at mimtarch.com>
> Dear All,
>
> I have a simple question. If we need to model natural draft boiler as
> required by G3.1.3.2 with the efficiency of 80% Et as given by Table 6.8.1F,
> does this mean that the HIR value in eQuest needs to be 1.25? Or are there
> some other intricacies that one needs to take into account here?
>
> Thank you for any replies,
>
> Ömer Moltay, LEED AP BD+C, BREEAM Assessor
> Mimta Ltd.
> Hekimsuyu Cad. 559. Sk. No:39
> 34255 Kucukkoy Istanbul Turkey
> Tel: 90-212-617-2296
> Fax: 90-212-617-2297
> www.mimtarch.com
> www.eko-yapi.net
> www.mimtasolar.com
> www.servogas.com
>
>
> ______________________________**_________________
> Equest-users mailing list
> http://lists.onebuilding.org/**listinfo.cgi/equest-users-**onebuilding.org<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE@**ONEBUILDING.ORG<EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110621/4c3b68cc/attachment.htm>
More information about the Equest-users
mailing list