[Equest-users] DOAS with changable volume!
Brian Fountain
bfountain at greensim.com
Tue Jun 14 05:50:27 PDT 2011
In the current version of eQUEST (3.64), "OA from system" isn't really
DOAS -- it is a temporary work around that has not been removed. I
understand it is high priority to fix in later versions. At present,
all that happens is the OA temperature for the borrowing system is set
to the return air temperature of the lending system. So, the air
volumes aren't really addressed -- although the air volume of the
lending system does get set up if the borrowing system OA volume is
higher. However at present (to my knowledge -- please correct this
those who know) the lending system does not look at the hourly OA values
so its volume will not change even if you turn DCV on for the borrowing
system.
Brian
On 6/13/2011 10:27 PM, tiejun hu wrote:
> Hi all:
> in my modle, in DOAS, I choose DCV return sensor, min fresh
> ratio=1, and not defined sum air volume of dummy zoon. i think the air
> number will vary with people number , but not. so who can guide me how
> to setup parameters so that air quantity change hourly. thanks
> BEST REGARDS
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1382 / Virus Database: 1513/3702 - Release Date: 06/13/11
>
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1382 / Virus Database: 1513/3702 - Release Date: 06/13/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110614/77a771ff/attachment.htm>
More information about the Equest-users
mailing list