[Equest-users] Primary/Secondary Loop Flow Reporting PV-A
    Seun Odukomaiya 
    SOdukomaiya at lacquis.com
       
    Thu Jun  9 09:01:43 PDT 2011
    
    
  
eQuesters,
I'm modeling a Primary/Secondary 2-pipe system in equest and am having issues with the PV-A report. The report shows the capacity and flow of my Primary loop as the sum of the capacities of all the attached equipment (boilers and chillers). I believe this is the correct way to report it.
The report, however, shows my Secondary loop capacity and flow as the sum of the capacities and flows of all the coils attached to that loop. This results in massive capacity and flows for that loop. The flow is about quadruple what my pumps are sized for, and I'm concerned that the LEED reviewer will flag this as an issue.
Is there a way to show the Secondary loop as the sum of the COINCIDENT loads on that loop? I have selected "PRIMARY" under the sizing option for that loop, but it still reports the sum of all the attached coils. I'm at a loss here and hoping that someone can help me out with this issue. I have attached my inp and pd2 files. Thanks in advance
Seun Odukomaiya, EIT, LEED AP | Mechanical Engineer | L'Acquis Consulting Engineers |(317) 706-2075 Ext. 255 | www.lacquis.com<http://www.laceindy.com/> | To transmit large files, please use:  http://lacquis.leapfile.net<http://lacquis.leapfile.net/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110609/a25d39c5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IPS School 79.inp
Type: application/octet-stream
Size: 494274 bytes
Desc: IPS School 79.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110609/a25d39c5/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: IPS School 79.pd2
Type: application/octet-stream
Size: 71706 bytes
Desc: IPS School 79.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110609/a25d39c5/attachment-0001.obj>
    
    
More information about the Equest-users
mailing list