[Equest-users] How to generate gas hourly consumption report from	EE4
    Brian Fountain 
    bfountain at greensim.com
       
    Wed Jun  8 07:30:47 PDT 2011
    
    
  
Try adding the following to the DOE-2.1e code, plant level:
REPSCH = SCHEDULE THRU DEC 31, (ALL) (1,24) (1)..
RB-1 = REPORT-BLOCK
     VARIABLE-TYPE = END-USE
     VARIABLE-LIST = (23, 28) ..
HR-1 = HOURLY-REPORT
     REPORT-SCHEDULE = REPSCH
     REPORT-BLOCK = (RB-1) ..
where variable 23 is the hourly electrical load in kW & variable 28 is 
fuel meter 1 (with default EE4 units of therms).
On 6/7/2011 4:19 PM, Xiangjin Yang wrote:
>
> Hello All
>
> Does anyone know how to generate gas hourly consumption report by 
> making report block in EE4 doe file?
>
> Thanks,
>
> *Xiangjin Yang *Ph.D.
>
> /Mechanical Designer /
>
> */MCW Consultants Ltd. /* <http://www.mcw.com>
>
> /156 Front Street West Suite 600
> Toronto, ON M5J 2L6
> Phone 416-598-2920
> Fax 416-598-5394 /
>
> /This e-mail may be privileged and confidential. Any unauthorized use 
> is strictly prohibited. If you received this e-mail in error, please 
> contact the sender directly. /
>
> PPlease consider the environment before printing this e-mail
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1382 / Virus Database: 1511/3686 - Release Date: 06/07/11
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110608/3efd0a92/attachment.htm>
    
    
More information about the Equest-users
mailing list